Discuss Rcd tripping on no trip Eli test in the Australia area at ElectriciansForums.net

hoover

-
Reaction score
3
Hi using a megger 1552 to do a few earth loops in a house. It's on the no trip function but still the rcd trips. Never had this before as usually the rcd holds out long enough to get the required reading for the earth loop imp. It's a tt system and the rcd ( 30 ma) is relatively new. Any thoughts?
 
have you tried the rcd tested alone without any circuits switched on, seen n/e faults cause rcds not trip and also a poor main earth (still never worked out why)

test rcd alone if same try a different one if it works start checking circuits
 
i would first do a ramp test on the RCD. you may have leakage just below the threshold, and your loop test is taking it over.
 
I dont think a low current loop guarantees that it wont throw the RCD when testing...my MFT will do just about every test you would need for installs ....but it wont do a low current Zs....I just wire out the RCD or just do the simple maths : Zs = Ze+ R1 R2..........
 
Last edited:
Hi using a megger 1552 to do a few earth loops in a house. It's on the no trip function but still the rcd trips. Never had this before as usually the rcd holds out long enough to get the required reading for the earth loop imp. It's a tt system and the rcd ( 30 ma) is relatively new. Any thoughts?

When this happens to me it's usually because I've done something daft like get the test leads mixed up so I've got E & N reversed or something!
 
just had a similar problem with a metrel. using the tester with 2 leads just Line and CPC it tripped the RCD using it as a 3 wire tester Line neutral and CPC it tested OK
 
What model Metrel?
I thought the Zs test with Metrels had to always be done with 3 leads?
Don't you have to join the E&N leads together?
 
Last edited by a moderator:
Hi Hoover, the Megger 1552 MFT Hi current loop test is 2 wire, but No-trip loop test is 3 wire, this often traps the unwary. Trying to 2 wire, No-trip test with the 1552 WILL TRIP out the RCD, due to unbalanced current injection/loading.
 
Last edited by a moderator:
Hi Hoover, the Megger 1552 MFT Hi current loop test is 2 wire, but No-trip loop test is 3 wire, this often traps the unwary. Trying to 2 wire, No-trip test with the 1552 WILL TRIP out the RCD, due to unbalanced current injection/loading.
When i read that post i thought he was getting mixed up with doing a PFC Markie....
 
Hi Hoover, the Megger 1552 MFT Hi current loop test is 2 wire, but No-trip loop test is 3 wire, this often traps the unwary. Trying to 2 wire, No-trip test with the 1552 WILL TRIP out the RCD, due to unbalanced current injection/loading.
Hi. I'm using the plug lead in the socket outlet to do my Eli so would imagine it's the three lead method ok.
 
Hi Spinlondon Metrel easitest with a A1176 2 wire tip commander use this for Zs and the RCD trips use standard 3 wire lead connected to L N and E and it tests OK. The tip commander is quick and easy for most tests except Zs with an RCD check out the metrel catalogue item A1176 Tip commander

METREL TECHNICAL CATALOG 2011
 

Reply to Rcd tripping on no trip Eli test in the Australia area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
911
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
1
Views
227
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
645
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
896
Having a bit of a brain freeze moment. I have a 2-core SWA cable running to an outbuilding. The sheath is used to earth this cable back to the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock