Hello,

I promised I’d give an update in hopes it would help somebody else one day.

So, after much back and forth with SSE they finally sent out an engineer. Straight away the engineer said that it’ll be the smart meter causing the RCD box to trip.

He proved it by calling head office and asking a colleague to take a reading. When they did, it tripped.

He ended up moving the smart part of the meter as far away on the board as he could and it hasn’t tripped since.

It did take me filing a complaint to get this resolved as SSE were telling me I had to pay for my own electrician first. Eventually they agreed to look into it. I was also awarded £130 compensation as this went on for a good couple of months.

Hope this helps somebody one day.

Thanks

Many thanks for letting us know.
 
Is that a gas or water pipe? Cables have to be at least 25mm away if it's gas.
Do you mean the pipe along the bottom that has the greenish yellow cables attached? I think that’s gas. The gas meter is off to the right where those pipes go.

I rent the property so not sure on the exacts, but my landlord does send out somebody to service my boiler and he does go into that area.
 
That 25mm distance is another meaningless regulation.The gas pipe is already part of the electrical system by virtue of been bonded to the MET.

I totally agree.

Isn’t that distance of 25mm a gas reg?

As I’m pretty sure there’s no distance specified in BS7671.
 
I totally agree.

Isn’t that distance of 25mm a gas reg?

As I’m pretty sure there’s no distance specified in BS7671.
OSG pg 25: 'Where gas installation pipework is not separated from electrical equipment or cables by an insulating exclosure, dividing barrier, trunking, or conduit, the following separation distances shall be observed:

a) 150mm away from supply equipment and
b) at least 25mm from sockets, switches, supply and distribution cables.

BS7671 tells you on page 152 that BS6891 tells you what to do in this instance. BS6891 tells you the same as the on site guide.

It's a requirement that we're not just allowed to ignore.
 
So we can ignore that one?
No we can,t.The regs are the regs and must be applied.What we can do though is look at the regs and put them in context and recognize that our regulators are learning too.That means that when we read a thread about a smart meter tripping an rcd we can be absolutely confident that it has nothing to do with a cable been "less than 25mm" away from a gas pipe.
I would love to sit in a room with a regulator to discuss who came up with these regulations and what is the basis for them.I have actually tried to. I won't bore you with details but let's just say it has,nt been very fruitful.
 

Reply to RCD tripping straight after smart meter install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
855
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
615
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock