Discuss RCD tripping time (in factory) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
Hi, bit confused, have an RCD Main Switch 250A with variable settings for mA and mS, now this is set at 1000mA, 1s time delay, I’m getting 99ms with set on 1000mA and no time delay my tester does not do 1s delay, now this board feeds another, so will I put 1099ms for tripping time?
I was just confused as I see max tripping time 500ms for a time delayed RCD somewhere could be wrong? It’s only a distribution circuit
Thanks
 
I don't think you want to add the tested tripping time to the delay set on the dial. If the tester will not provide a 1 second test, you cannot show that the RCD trips correctly as set, so you cannot complete that test as such.

The maximum permissible delay setting depends on what protection it is providing. For a distribution circuit on a TT installation I believe 1s is the norm.
 
So is the RCD tripping in 99mS? Or is it not tripping and the tester is showing >99mS as they often do to indicate that it has not tripped.

If it has tripped in 99mS then the delay isn't working.
If it has not tripped then you can't record any time for it because it hasn't operated.

You could adjust the time delay for the test so that it falls within the abilities of the tester, this will at least prove that the RCD works, but it won't prove what it does at its cirrect settings.
 

Reply to RCD tripping time (in factory) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
888
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock