Discuss RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

K

Kingston555

Recently, whenever we plug in either our kettle (1850-2200 Watts) or our iron (2300-2750 Watts), it trips the RCD for that circuit. Nothing has been changed on the installation, and we've had both appliances for a few years and they never used to cause this problem. Up until recently, whenever the RCD did trip, I simply re-set it and then we were able to use whichever appliance it was. However, this morning there was a loud pop when the missus plugged in the kettle, and now the kettle won't work at all, despite me changing the fuse in the plug. Also, the socket which she plugged it into won't work either: the switch is stuck in the open position. Any ideas welcomed.
 
what he said. ^^^^. it would appear that the kettle has been faulty for a while, getting progressively worse, till finally shorting out.
 
The RCD tripping was indicative of the appliances started to fail, although it could also be indicative of the socket starting to fail but this less likely to occur in this manner.

The bang and the total failure of the kettle caused a high fault current to flow and this spark welded the contacts together (or melted the plastic of the switch) so that the switch will not operate.

As said above the kettle is now broken and the socket is damaged and both need replacing.
 
what he said. ^^^^. it would appear that the kettle has been faulty for a while, getting progressively worse, till finally shorting out. drink beer till you get a replacement.
 
The RCD tripping was indicative of the appliances started to fail, although it could also be indicative of the socket starting to fail but this less likely to occur in this manner.

The bang and the total failure of the kettle caused a high fault current to flow and this spark welded the contacts together (or melted the plastic of the switch) so that the switch will not operate.

As said above the kettle is now broken and the socket is damaged and both need replacing.

Another good word to add to my repertoire,Rich "Indicative" nice one must try and fit that one in somewhere.
 
Thanks to all for the feedback, but one thing that's puzzling is that the kettle is only about a month old and carries the CE mark. Is it common for such an appliance to fail so soon?
 
if your kettle is only a month old it will still be guaranteed so take it back to where you got it but how about the iron is it still making your RCD trip or was it just your socket ?
 

Reply to RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
807
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
743
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock