Discuss Rcd tripping in the Australia area at ElectriciansForums.net

F

Fender

Hi all, Got a tt system and rcd trips when all circuits are on after a couple of minuites. Only trips when the garage mcb is on with this isolated all other circuits seem ok but turn on garage and 5 minuites later rcd (which is main switch) trips and wont reset without turning all circuits off first. There are no loads on in garage except lights. Any ideas would it b garage circuit (on its own) causing problem perhaps a phase to earth fault. There is an outside halogen on the circuit but with the switch to this off in the house rcd still trips. Have not yet tried insulation test. Thanks for reading.
 
water ingress in halogen light is a possible. suspecy N/E leakage somewhere in or around garage. you really have to IR test
 
sorry can't edit. go logically and IR test supply cable to garage with loads disconnected. then if that's ok break it down till you find the culprit.
 
Really need to get those IR tests done, to eliminate or confirm circuits statuses. This is another of those occassions where a mA leakage clamp meter would be well worth having to hand!!
 
halogen will cause tripping when off if it's a N/E fault. disconnect both L and N. then see if it still trips.
 

Reply to Rcd tripping in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
508
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
605
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
383

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock