Just been called to a tripping problem in a lab,where 3 seperate rcds would trip out for no reason.After some time discovered a heat damaged neutral connection in a seperate db in another part of the building.With this connection repaired ,the tripping problem ceased.Can any one explain this .:dizzy2:
 

Reply to rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
580
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
471

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock