Discuss Rcd in the Australia area at ElectriciansForums.net

L

lamb.a

We are suppling an outside portacabin with a steel wired armoured 3 core cable live neutral earth from a TN-S system. Does the portocabin reguire an earth electrode and does the origin of the supply have to have an rcd/rcbo fitted with a rcd and also fitted on the consumer unit inside the portocabin.
 
Hey.

We do a lot of portacabins for local schools and the way I do it for TN-S is 25mm3c swa protected by 100mA RCD and 60A switchfuse at the origin then terminated into whatever board is in the cabin. Usually the board in the cabin has a 30mA rcd up front as main switch, I then bond everything back to my DB in the cabin i.e water, gas, steelwork etc, as the 25mm CPC in the swa is sufficient to carry any fault current back to the main intake un the school and de-energise the supply.

For TN-C-S, I do turn them into TT installations i.e 25mm2c and drop a 25mm earth down to my rod, the rest is the same.

Hope this helps.
 

Reply to Rcd in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
746
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
669
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock