Search the forum,

Discuss RCD's in series in the Australia area at ElectriciansForums.net

There's always a way. If you can't do the job properly don't do it. A good reputation is hard earned and easily lost.

Do you have any photos of this concrete bunker?
 
I have been doing some testing work on a Nursing Home (new client) which had two 30ma RCDs in series (1 x DB supplying 5 x DB's approx 40m appart) and while testing it was tripping at both RCDs 1 x on one and 5 times on the other really annoying as made testing awkward ! Not ideal.

Back to original scenario of outside supply I always put the outside supply on the non RCD side of the board supplied via a RCBO 100ma and 30ma at shed CU this gives full discrimination for the outside circuit. How do the rest of you do it?
 
I always put the outside supply on the non RCD side of the board supplied via a RCBO 100ma and 30ma at shed CU this gives full discrimination for the outside circuit.

Are you sure about that?

What are you doing when you're testing at x5 on RCD test?

You would need a time delayed RCD as I understand it from reading posts on the forum?
 
Im really intrested in this, anyone got a technical reason or idea why this could happen?


Faulty RCDs? Cannot see any other reason theres no magic secret with them as far as Im aware. Needasparks what do you mean you had discrim. with two 30mA RCD's?
 

Reply to RCD's in series in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
901
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
583
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock