I am quoteing to change an old consumer unit to 17th edition on a TT installation. I have checked the regs and it looks like the preffered option is to give added protection by changing the 100A main switch to a 100A 100mA RCD together with the 30mA RCD protection already in the board. Firstly is this correct or havr I miss read it? and secondly I believe (though I will have to double check) that the supplier or previous sparky has fitted an RCD as an isolation device before the board. I have no idea of its age so should I rely on it. I geuss testing it both manually and electronically will give me that answer?

Many thanks in advance
 
100ma rcd if the board is metalclad to protect the tails otherwise dual rcd 17th edition board 'plastic' with 100a main switch is fine as direct replacement. the two 30ma rcds will cover all circuits with protection required.
 
A single RCD protecting a TT system must be installed at the origin of the installation unless the part of the system between the origin and the RCD fulfills the requirements for protection by Class II equipment or equivalent insulation. 531.4.1
 

Reply to RCD's In TT Systems in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
880
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock