Discuss RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

S

Sparkz123

Hi,

I have a problem with 17t edition consumer unit (MK Sentry) on a TT system that has completely left me baffled. I'd be very grateful for an advice.

On the left hand side of the board I have a 100 amp main switch. Immediately next to that a 30ma RCD controlling 3 MCB's and 2 spare ways, followed by a second MCB controlling 4 MCB's and one spare.

If I test the3 left hand circuits the L/H RCD fails to operate, it also fails to operate when tested from the board. If I test any of the circuits controlled by the R/H RCD both RCD's trip. If I swap the RCDs around nothing changes, the L/H one fails to operate unless the R/H one is tested.

All my neutrals are connected to the correct connector blocks and there are no IR readings between the two blocks.

To leave the entire installation RCD protected overnight I swapped the main switch and L/H RCD's around, so the main switch was an RCD, but this failed to operate, even though it was fine when controlling the L/H circuits.

I'd appreciate any input.

Thanks,

Pete.
 
Disconnect all circuits from the board and carry out RCD tests with prods , see what happens , if all works correctly for both RCDs then its an issue with your wiring , or faulty RCDs ,
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.

probably decided to trip at last and take the lights out.
 
Any chance of a picture of the CU close up I take it you have checked and double checked that its connected up correctly !!!!

Just out of interest what is your RA at the board ?
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.

That seems a bit of a coincidence, what was the outcome? Was it a faulty RCD or something else?

I'm confident that there are no shared neutrals, I have tested between the 2 neutral blocks and the readings were clear. It's not a new installation, I've just replaced an old board covered by a voltage operated trip. I'll disconnect all the circuits tomorrow and see what happens but I can't think of a wiring fault that could cause this. If it fails to work properly once the circuits are disconnected it's got to be a fault on the boards internal wiring, but God knows what.

Thanks everyone for the input.
 
I'll get a picture tomorrow Tony. I don't recall the exact rA but it was nothing out of the ordinay, I'll make a note of it when I certify it
 
That seems a bit of a coincidence, what was the outcome? Was it a faulty RCD or something else?

I'm confident that there are no shared neutrals, I have tested between the 2 neutral blocks and the readings were clear. It's not a new installation, I've just replaced an old board covered by a voltage operated trip. I'll disconnect all the circuits tomorrow and see what happens but I can't think of a wiring fault that could cause this. If it fails to work properly once the circuits are disconnected it's got to be a fault on the boards internal wiring, but God knows what.

Thanks everyone for the input.

Same thing, replaced board in brother in law's house, up front VO trip and re-wireable board, two new rings to give adequate sockets outlets in bedrooms and lounge, also to overcome lose of earth in lounge sockets. Come to test and one RCD won't trip. Faulty RCD. Also the mcbs wouldn't sit straight, and the factory wired neutral links came loose from the crimped lugs.

Horrible board, won't ever use another through choice.
 
Same thing, replaced board in brother in law's house, up front VO trip and re-wireable board, two new rings to give adequate sockets outlets in bedrooms and lounge, also to overcome lose of earth in lounge sockets. Come to test and one RCD won't trip. Faulty RCD. Also the mcbs wouldn't sit straight, and the factory wired neutral links came loose from the crimped lugs.

Horrible board, won't ever use another through choice.

was that a MK board by any chance?
 
An RCD that fails to trip by its own test button or an MFT while installed but works OK on the bench or with all circuits disconnected, usually indicates an N/E fault on the installation downstream. This causes the test button current or MFT test current to 'miss' the N side of the RCD by running to earth. In your case it suggests a fault on the L/H group of circuits, which I recommend re-testing.

I'm guessing the L/H RCD trips when using the MFT to test the R/H one but not with the test button? If so, this corroborates it as an N/E fault, as the R/H test button doesn't cause current to flow in the CPC and hence doesn't influence the L/H one. But the MFT dumps the test current to the CPC, some of which ends up returning via the L/H RCD neutral and tripping it.
 
The old LN sentry range from the 80s and 90s were good , but this new stuff is not , the sockets get me , has anyone noticed how tight the terminal screw threads are , a customer had some for me to fit for him ...
 
Last edited by a moderator:
High integrity board by any chance?? I've seen them come wired wrong. Outgoing neutrals in wrong bars etc.

Have you got any dead shorts neutral to earth on the connected circuits? Could prevent the rcd from operating when testing.
 

Reply to RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
887
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock