Discuss RCDs tripping feeding Megaflo heating elements in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Got 2 32A RCDs in a CU, each one feeding a respective Megaflo water heater circuit.

At the Megaflo each stat head is wired back through a timer and onto a fused spur. RCD is tripping straight away with cables connected to the stat and stat into element. Dissconnect stat from element and it doesn't trip the RCD.

IR on element gives me 0 between conductors and > 275M Ohms conductor to earth spade.

Originally we changed both heating elements and stats, but the RCD is still tripping immediately. It would appear the fault lies with the element/s but they're brand new!
 
Sigh, N>E?

Edit: Didn't see that they could well be RCBO's, what KW rating are the elements?
 
Last edited by a moderator:
The issue will be a simply one and one you will have overlooked, the problem for us if you have overlooked it then you will not have given us all the relevent info for us to see the issue ... can we clear up a point - you say you disconnect the stat and the rcd don't trip, when you disconnect the stat have you connected the elements direct without the stat in the loop or just left the circuit open....

Also are we sure the voltage and rating of the elements is correct for the supply your using?
 
... can we clear up a point - you say you disconnect the stat and the rcd don't trip, when you disconnect the stat have you connected the elements direct without the stat in the loop or just left the circuit open....

Also are we sure the voltage and rating of the elements is correct for the supply your using?

no I haven't connected the active and neutral directly to the spades on the element if that's what you mean. I'm sure the RCBO will trip immediately if I do this as it does so as soon as the stat is pushed in with said cables connected.

2.7-3KW single phase element with a 32A RCBO..
 
Are you saying that 1 x megaflow, 2 x immersion circuits, each supplied by seperate circuits, off seperate RCD's??

Do both RCD's trip?

Just asking

Yes sir, that is the situation.

Problem solved now, turns out the sub circuit tales had been swapped around in the CU!

thanks for everyone's suggestions and advice!
 

Reply to RCDs tripping feeding Megaflo heating elements in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock