Background
Elderly relative asks neighbour to change the bathroom ceiling lightbulb.
Neighbour starts to change lightbulb, drops and breaks fancy lampshade so fits a replacement ceiling rose.
(Old rose wouldn't take a standard lampshade fitting.)
After fitting the ceiling rose and checking the bathroom light now works, neighbour disappears.

Today
Relative switches on hall light just outside bathroom. The hall and bathroom lamps both glow at what appears to be half power.
Then switches the bathroom light on and the bathroom light is normal brightness, the hall light goes off.
The bathroom light works normally without the hall light being on.

Connections
The connections, as I can work out, are in the attached diagram.

What has the neighbour done? What needs to be done to get things working normally?
 

Attachments

  • bathroom_ceiling_rose_connections.png
    68.5 KB · Views: 50
If your diagram is correct it looks like the hall switched live is actually the neutral to the hall light and just needs moving to the terminal with the other black wire. Switching the hall light puts the two lamps in series causing them to light at half brightness switching the bathroom light bypasses the hall light
 
Hi, thanks for your reply.

I've disconnected the two connections I've shown as switched lives and checked that one goes live when the bathroom light is switched on and the other goes live when the hall light is switched on.

You say that the hall switched live could be the hall neutral. Where should this be connected?
 
You need to check continuity of all those cables before going any further. Swapping cables around willy nilly not knowing what is a neutral or live is going to lead to a loud bang and a fried switch!

Sorry to be blunt, but there’s too many configurations of lighting methods for any of us to say 100% what goes where. After the neighbour makes one mistake, that’s any logical ideas out the window.

I see you know electricity from your profile, so you know about loud bangs, but I would, this time, suggest you get an electrician to look at it. 30 minutes tops.... 10 minutes to fix, and 20 for a cup of coffee.

Where in UK? Maybe a forum member nearby
 
Read the previous post, the 'blacks' are mixed up. Connect the neutrals together. Then a bit of checking and advice.
Any recompense for the fancy lampshade?
 
try taking it out of the left terminal and stick it in the right side one. worst scenario is you trip the MCB. commonly known as the bang test, used mainly in USA. :p :p :p .
 
Thanks all for your comments.

Thinking about this, given that the hall switch is lighting (half lighting) the bathroom and hall lights, the switched hall live must be going through the hall light first. In which case, it's not actually the true switched live but a floating live expecting a neutral?
It would seem that the apparent switched hall live should be moved to the other side of the bathroom lamp i.e. the neutral.

Thoughts?
 
Thanks all for your comments.

Thinking about this, given that the hall switch is lighting (half lighting) the bathroom and hall lights, the switched hall live must be going through the hall light first. In which case, it's not actually the true switched live but a floating live expecting a neutral?
It would seem that the apparent switched hall live should be moved to the other side of the bathroom lamp i.e. the neutral.

Thoughts?
Get an electrician to look at it, clearly your struggling with a basic job and you could end up in a hole you cannot climb out of
 
'return'...................to #2.
OP, take some advice regarding safety.
You're thinking along the right lines, terminology astray. Remember, getting something to work correctly is minor when compared to safety issues.
 
Thanks all for your comments.

Thinking about this, given that the hall switch is lighting (half lighting) the bathroom and hall lights, the switched hall live must be going through the hall light first. In which case, it's not actually the true switched live but a floating live expecting a neutral?
It would seem that the apparent switched hall live should be moved to the other side of the bathroom lamp i.e. the neutral.

Thoughts?
You are correct remove the lamp in the hall and the hall switched live will no longer be a switched live when you turn the hall light on, connect to the neutral job sorted
 
UNG, I realise now you were spot on in your original post. I just needed to work that through. Thank you.

And thanks everyone else. I take the safety first comments on board.
 
It's nice when someone hits the nail squarely on the head in post #2, which in two sentences not only says what happened but also how to fix it and why it behaves as it does. We often go all round the houses with 'what testing have you done' etc. and quizzing for lots of extra info, but when just one (highly probable) scenario exactly fits the symptoms, it's worth offering up sooner rather than later.
 
however, the current wiring allows OP to have 2 lights on for the running cost of one (albeit dim). :p :p
 

Reply to Re-wired bathroom ceiling rose causing bathroom and hall lamps to glow 'half' power in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
701
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
924
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
569
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock