knock on the door last night.
“Could you have a look at my electrics. Sockets off, cooker working. Managed to get telly on with an extension lead.”
They couldn’t really say what happened, just that the switch wouldn’t reset.
So walking distance job, find that they’ve had a new db in 2016... rcbo’s all circuits. Downstairs sockets only are off.
However. All tools and testers are in my storage as I’m on holiday now, so that was a 4 mile drive before I get started.
Testing circuit brings up L to E short. So I start splitting the ring. A few likely points where additions have been made or rawlplug holes in the vicinity of where vertical cables runs are.
Problem found in kitchen where a single socket had been spurred from another single... the newish faceplate was the cause.... dead short between the L and E terminals.
So I was there about an hour, plus the drive out and back. Finished at 10pm.
£50 call out plus my usual hourly rate or should I be a little more severe.
No talk of money beforehand, but I did say there would have to be a callout charge.
“Could you have a look at my electrics. Sockets off, cooker working. Managed to get telly on with an extension lead.”
They couldn’t really say what happened, just that the switch wouldn’t reset.
So walking distance job, find that they’ve had a new db in 2016... rcbo’s all circuits. Downstairs sockets only are off.
However. All tools and testers are in my storage as I’m on holiday now, so that was a 4 mile drive before I get started.
Testing circuit brings up L to E short. So I start splitting the ring. A few likely points where additions have been made or rawlplug holes in the vicinity of where vertical cables runs are.
Problem found in kitchen where a single socket had been spurred from another single... the newish faceplate was the cause.... dead short between the L and E terminals.
So I was there about an hour, plus the drive out and back. Finished at 10pm.
£50 call out plus my usual hourly rate or should I be a little more severe.
No talk of money beforehand, but I did say there would have to be a callout charge.