Hi guys what do you think of this. There’s been a temporary bit of plant wired up out of an existing circuit which is an 100amp supply I believe. The circuit then goes through a soft start to a local isolator about 50meters away. The motor is supplied with 10mm flex but due to the flex not being long enough someone has used a JB and extended to the isolator with 6mm flex. My thoughts are the 6mm is a bit close as the motors FLC is 41 Amp. I’m also aware the main fuses are 100amp so again oversized. Another question was the overload was set to 41 amps I know this isn’t ideal to rely on but would the cable be protected?


thanks guys
 
The thermal relay will limit the current flow what it won't do is offer short circuit protection. Is it single or three phase.
 
Hi guys what do you think of this. There’s been a temporary bit of plant wired up out of an existing circuit which is an 100amp supply I believe. The circuit then goes through a soft start to a local isolator about 50meters away. The motor is supplied with 10mm flex but due to the flex not being long enough someone has used a JB and extended to the isolator with 6mm flex. My thoughts are the 6mm is a bit close as the motors FLC is 41 Amp. I’m also aware the main fuses are 100amp so again oversized. Another question was the overload was set to 41 amps I know this isn’t ideal to rely on but would the cable be protected?


thanks guy
The thermal relay will limit the current flow what it won't do is offer short circuit protection. Is it single or three phase.
Sorry it’s 3 phase
 
That is a YY cable and a four core 6.0 will carry 44A
Thanks westward10 so ideally we’d want to install 40 amp fuses to protect the cable? Also just curious why won’t an overload pic up a short as I thought the overload will pick up the overcurrent and trip or is it more todo with the delay on the overload?
Thanks
 

Reply to Reduce cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K
Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused...
Replies
4
Views
2K
Evening All, Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board...
Replies
4
Views
1K
Ok so the scenario is there is an old MICC or pyro 1.5mm 2 core cable supplying the garage run underground on a 16A circuit breaker that is RCD...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock