Refused Connection

Discussion in 'Solar PV Forum' started by jason121, Jul 7, 2014.

Discuss Refused Connection in the Solar PV Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    Had my first refusal today for 50 KW system due to western power primary sub station not able to with stand all the Solar PV in the area.
    I have to wait for the upgrades in a few months.

    To much reverse power anyone else experience this yet
     
  2. a1colly
    Offline

    a1colly Regular EF Member

    Location:
    Merthyr Tydfil
    Not yet, didn't you get it connected within the written agreement timescales? I was always under the impression you didn't get an accept unless the upgrade work had been completed and no other connections were allowed until your offer had expired.
     
  3. driverman
    Offline

    driverman DIY

    Location:
    England
    Should you /customer of informed them before you started? At least there is an upgrade coming later. What would of happened if no upgrade being planned?
     
  4. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    Paper work stage not installed yet.
     
  5. driverman
    Offline

    driverman DIY

    Location:
    England
    Ahh good then. So all is not lost then , especially with upgrade on the horizon.
     
  6. a1colly
    Offline

    a1colly Regular EF Member

    Location:
    Merthyr Tydfil
    Ahhhh that's good, had plenty of them currently sitting on a £65k upgrade for 24kwp - 1.7kwp system x 20 and the client has agreed to pay
     
  7. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    The govt want all these roof top mounted solar but the grid cant cope
     
  8. Worcester
    Offline

    Worcester Forum Mentor

    Location:
    Worcestershire
    Yep had one refused in Leciestershire not so long ago (200kWp) got around it when we agreed not to export >3.68kW per phase :)

    We estimated the total cost to the business based on matching their half hourly consumption data to half hourly generation data predictions was less than 4% so the project was still a goer :)
     
  9. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    What make and type did you use to limit current capacity
     
  10. Energetic
    Offline

    Energetic Electrician's Arms

    Location:
    South West
    We've had 30kw turned down in devon as it's not far from a multi-acre solar farm. Have been told by WPD that Devon and Cornwall is 'full'. Unlikely to be any private upgrades that will fix it, they reckon it will take billions in infrastructure upgrades.
     
  11. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    Time to burn your tool box and retire
     
  12. snowhead
    Online

    snowhead Respected Member

    Location:
    Mildlands
    The solution would be to encourage some heavy (power consuming) industry into the area.
     
    • Like Like x 1
  13. Gavin A
    Offline

    Gavin A Electrician's Arms

    Location:
    Leeds
    Business Name:
    Leeds Solar
    we use power one with the PMU unit to control it, and elios 3 phase unit for the actual export limitation... it works, but waiting for a firmware upgrade to actually lock the setting.

    currently only does up to 100A supplies though due to the CT clamps, another thing on my list to get sorted....... (looks at Andy Sibert)
     
  14. jason121
    Offline

    jason121 Electrician's Arms

    Location:
    Lincolnshire
    Spoke to Andy about the elios upgrade for 100 amp plus they have no intention yet to do so.
    I need to limit 200 kw plus
     
  15. shanky887614
    Offline

    shanky887614 Electrician's Arms

    Location:
    Castle Donington
    if it is limited to 100amp.

    can't you split the strings?

    it might add a bit more with the cost of inverters etc but surely that would make it possible then
     
Loading...
Similar Threads - Refused Connection Forum Date
Currys refused to install my daughter's cooker, but.... Electrical Appliances Forum Nov 26, 2018
Ax disconnection times 32A+ Electrical Course Trainees Only Thursday at 6:12 AM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job