Discuss Regs guide typo or not? - what is allowed disconection?! in the UK Electrical Forum area at ElectriciansForums.net

I

Inteificio

For disconection times we have to hit 0.4 for up to 230v U0. 0.2 for 400-1000U0.

I always took this to mean what it says.

both single and 3 phase V to earth is 230, so we use the 0.4 disconection.


Taking my 17th update and got told that was a typo!!!!

So for 3 phase we are supposed to use 0.2, single 0.4.

Now that is not what the book says!

So what am I supposed to design my circuits for?!

The question is partially moot as I always use MCBs so they knock off in 0.1, but that is not not the point.

When I chuck in my next 88, what should I desgin it too?
 
Given that the power dissipated in a phase to phase fault is 3 times that of phase to neutral a faster disconnection time makes sense.
 
For disconection times we have to hit 0.4 for up to 230v U0. 0.2 for 400-1000U0.

I always took this to mean what it says.

both single and 3 phase V to earth is 230, so we use the 0.4 disconection.


Taking my 17th update and got told that was a typo!!!!

So for 3 phase we are supposed to use 0.2, single 0.4.

Now that is not what the book says!

So what am I supposed to design my circuits for?!

The question is partially moot as I always use MCBs so they knock off in 0.1, but that is not not the point.

When I chuck in my next 88, what should I desgin it too?

There is no 'typo' it's 0.4 seconds and it is Uo.
 
Sorry for the late response. forgot to subscribe to this thread so didnt know there were any responses.

If it is not a typo then why the split?

I can undestand 230-400-1000v as that would be single phase, 3 phase and high voltage.

So why do they split it Uo for 230 400 and 1000?

Regs book is in the car so can't quote precise reg yet.

Just took my 17th 1st edition update today, there are quite a few changes!
 

Reply to Regs guide typo or not? - what is allowed disconection?! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
627
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock