Hi,

Need to have emergency stop switches for a workshop that will kill all the power

Looking for a remote control MCB or similar that can be added to distribution panel to enable a complete mains ring to be isolated from one or more push buttons around the workshop

I am unable to find such a solution online

Any ideas?

Thanks
 
Suitably sized contactor up front of DB controlled by em stop buttons situated at intervals around your workshop
 
Might be better using the contactor in the feed to the ring - this would avoid all the lights going out. Daz
 
A plain and simple contactor is all you need on the Ring final circuit after the MCB /RCBO plus EM stop buttons.

Is the EM stop circuit for convenience or to comply with a Reg?
 
Sorry have to say kill the supply, let the EM lights take over until it's sorted, see the point of only killing the sockets, but Nah take it all out of the equation imo.
 
Thanks

I had already looked for a solution like that but could only find solutions using safty rated PLCs which is over the top for my needs

I will look again

You do not need a PLC for emerency lighting. Just a feed with permanent live, when the live goes off they change into battery operation.
 
Good point amlu. Plc for em lighting? Different. Daz.
 
Kill 'Em All contactor sounds better than a contactor on a ring, the place may have couple of dedicated radials for powering machines...
 
Not sure why the EM Stops would need to do anything with the lighting at all? Surely just a contactor or contactors for the machines. If EM Stops killed the lighting then if anything it's also creating a hazard also
 
123 has it right. Kill the machines, not the lighting. Need to see things when somethings gone t*ts up. Daz.
 
Start from basics.
WHY, do you "NEED" the emergency stop?
Are you trying to comply with some sort of legislation or standard, or is just because you would like to have one in your home hobby workshop which is not for business use?
 
Hi,

Need to have emergency stop switches for a workshop that will kill all the power

Looking for a remote control MCB or similar that can be added to distribution panel to enable a complete mains ring to be isolated from one or more push buttons around the workshop

I am unable to find such a solution online

Any ideas?

Thanks

To remotely trip an mcb you need to add a tripping auxiliary to the mcb, either a shunt trip or an under voltage release depending on your act requirements.
At first glance I would have thought an under voltage release would be more suited to an emergency switching setup than a shunt trip.
But I think you need to take a step or two backwards and establish the details of exactly what you need, which could include risk assessments and a lot of research into statutory legislation.
 

Reply to Remote Control Mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

And now for something completely different! I have been after a power station telegraph for decades and due to the fact most would have been...
Replies
7
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
  • Article
Autumn is now here, it's that time of year where the clocks go back and lighting control moves forward. A time when UK customers with gardens want...
Replies
2
Views
727
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
929
I have a ceiling fan which currently has a remote control for fan speed and dimming the attached lights. We're currently doing some works in the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock