Hi,

Our old oven was plugged into a standard socket behind the adjoining unit with a 13amp fuse standard plug, the hob has it's own isolator box connected to the consumer unit - I'm presuming the socket the oven was plugged into is the down ring but I'm not certain (chef not electrician here!)

I took the plug off the old oven and wired the new oven to it, plugged it in and everything seems to be working fine - my worry now is that I've read the specifications on the new and old oven and the new oven is different.

The old oven was 230v 50hz 2980w

The new oven is 220-240v 50/60hz 2200w

I'm worried that

1) the 13amp fuse is too powerful for the appliance and
2) surely the oven shouldn't have been on that ring in the first place?

Any advice would be brilliant, losing the oven this close to Xmas already has my wife stressed as it is and I just want it right.

Cheers

Alan
 
if the old oven worked with no problems, the new one will be fine. it's 25% less load. if you are concerned, a quick visit by a local sparks would allay your fears.
 
Hi,

Our old oven was plugged into a standard socket behind the adjoining unit with a 13amp fuse standard plug, the hob has it's own isolator box connected to the consumer unit - I'm presuming the socket the oven was plugged into is the down ring but I'm not certain (chef not electrician here!)

I took the plug off the old oven and wired the new oven to it, plugged it in and everything seems to be working fine - my worry now is that I've read the specifications on the new and old oven and the new oven is different.

The old oven was 230v 50hz 2980w

The new oven is 220-240v 50/60hz 2200w

I'm worried that

1) the 13amp fuse is too powerful for the appliance and
2) surely the oven shouldn't have been on that ring in the first place?

Any advice would be brilliant, losing the oven this close to Xmas already has my wife stressed as it is and I just want it right.

Cheers

Alan
What or how does the new cooker's instructions state hoe it should be connected, the 13 Amp fuse cannot be to powerful for the cooker, as Tel said in post#2
 
if the old oven worked with no problems, the new one will be fine. it's 25% less load. if you are concerned, a quick visit by a local sparks would allay your fears.

Thanks for the swift reply, the manual says the oven should be earthed (which is wired up in the plug so I'm guessing that's not a problem) but it says it should be "wired into a 10A double pole switched fused spur outlet" - will my like for like swapping and using the same socket as the previous oven (worked fine for 10 years, then last week when we used the grill then turned the oven off it tripped the consumer unit - this fault was reproducible which led us to replacing it) be ok do you think?

Again, cheers!

Al
 
What or how does the new cooker's instructions state hoe it should be connected, the 13 Amp fuse cannot be to powerful for the cooker, as Tel said in post#2

Thanks for replying, I wrote the cooker's instructions above in post 3. My main concern is if there's a problem with the cooker, will the 13amp fuse in the plug not fuse because the cooker because it requires a 10.1amp fuse or will my (6 month old) consumer just trip?

Cheers,

Al
 
"wired into a 10A double pole switched fused spur outlet"

Al

I suspect that’s a bad translation by a foreign manufacturer, or just a lack of knowledge on their part.

Switched fused spurs in the uk use the same fuses as 13A plugs which are commonly available in 3A, 5A and 13A sizes, 10A fuses do exist but are very rare as in practice the difference between them and a 13A fuse is negligible.
 
Thanks very much guys, I tested it with a pepperoni pizza last night (best test of a new oven = pizza, you can see from the colouration of the cheese where the hot spots are) and the house still stands! :)

All the best to you and yours,

Al
 

Reply to Replaced an integrated oven, advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
798
Hi, I've recently had my broken oven replaced in my flat and I paid for delivery and installation. It was hardwired through an unswitched plate...
Replies
7
Views
1K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all, Our kitchen is going to be ripped out and replaced in the new year, and currently has just one small oven in it - I have 10 guests for...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock