Discuss Requirements for drilling holes in joists in the Australia area at ElectriciansForums.net

S

stuart569

Could anyone point me in the right direction for requirements to drilling joists? eg. distance out from end of etc... Have used a guidance sheet before but really dont have the time to trawl google searching for regs.
Cheers
 
center line more than 50mm from bottom and top of joist then in a zone between 0.25 and 0.40 x span
hole is 0.25 x joist depth notch 0.125 x joist depth ,notches 0.07 and 0.25 x span
 
Last edited by a moderator:
Page 119 'Electricians guide to the building regs'

*Notches on top of joist in a zone 0.07 and 0.25 x joist span.

*Max depth of notch should be 0.125 x joist depth.

* Holes on centre line of joist in a zone between 0.25 and 0.4 x joist span.

* Maximum diameter of hole should be 0.25 x joist depth.




Easier to understand with a diagram, but I hope that helps.

Regards.
 
Last edited by a moderator:
Part of the reason I ask is the plumber has staggered his holes diagonally. 4 holes in total and totally screwed my main clipping run.Its a new build
 
Building Regs Part A (Structure)
It's in diagram form in the Electricians Guide to the Building Regs.
The plumber should be working to BRs just the same as you. Report it to the site manager perhaps.
 
Regulations 522.6.5 – Impact (AG), Cables installed under floors or above a ceiling
Generally, a cable should either be:
i. installed ≥ 50 mm vertically from the top, or bottom as appropriate, of the joist or batten,
ii. incorporate an earthed metallic covering (e.g SWA, MICC etc.),
iii. be enclosed in earthed metallic conduit, trunking etc.),
iv. be provided with mechanical protection to prevent the penetration of the cable by nails, screws and the like
 
Glad I rewired my 1st house before the 15th edition at one point there was 40 cables running under the landing floor! From 1.0mm up to 16mm.
 
Glad I rewired my 1st house before the 15th edition at one point there was 40 cables running under the landing floor! From 1.0mm up to 16mm.

You still might be if you jump up and down too much........
 
Last edited by a moderator:

Reply to Requirements for drilling holes in joists in the Australia area at ElectriciansForums.net

Similar Threads

So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
709
Most of the work I do is additions and alterations in domestic properties, and other than swapping accessories and lights in new-builds for...
Replies
2
Views
2K
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi, Currently working my way through my NVQ portfolio (Nearing Completion) but getting stuck on how to complete the following criteria due to...
Replies
0
Views
962

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock