Markrobert30

Hi All first post.

I'm currently doing a Pre Entry in Electrical Engineering and really enjoying it so far.
My question is i'm finding the Resistors in Parallel a bit tricky see below.

The question asks me to determine the values of V,I2,I3 and R

Suppose i'm more confused in whats best to workout first

I've attached a Jpeg of it so you can see it i've written in the answers as they were on the sheet but if anyone could help i'd be really grateful.

Image below also.

Thanks

Mark

20131007_214507[1].jpg
 
This isn't really working out resistance in parallel more a case of ohms law.
First thing I would work out is V using the value of R1 and the current across it. V = I x R,
V = 10 x 5 so V = 50.
Then knowing the voltage you can work out the current I2 using I = V / R, I = 50 / 10 so I2 = 5A.
Lastly for I3 you know you had 40A to start with and you have 10A across R1 and 5A across R2 leaving you 25A across R3. Then use R = V / I, R = 50 / 25 so R = 2 ohms.

Hope this helps.
 
This isn't really working out resistance in parallel more a case of ohms law.
First thing I would work out is V using the value of R1 and the current across it. V = I x R,
V = 10 x 5 so V = 50.
Then knowing the voltage you can work out the current I2 using I = V / R, I = 50 / 10 so I2 = 5A.
Lastly for I3 you know you had 40A to start with and you have 10A across R1 and 5A across R2 leaving you 25A across R3. Then use R = V / I, R = 50 / 25 so R = 2 ohms.

Hope this helps.

Hey Sintra

That's perfect thank you think i was just getting myself confused with what to workout first. But your workings make it look so easy.

Mark
 
This isn't really working out resistance in parallel more a case of ohms law.
First thing I would work out is V using the value of R1 and the current across it. V = I x R,
V = 10 x 5 so V = 50.
Then knowing the voltage you can work out the current I2 using I = V / R, I = 50 / 10 so I2 = 5A.
Lastly for I3 you know you had 40A to start with and you have 10A across R1 and 5A across R2 leaving you 25A across R3. Then use R = V / I, R = 50 / 25 so R = 2 ohms.

Hope this helps.

<pedant> Current flows through a resistor, not across it eg "you have 10A flowing through R1." You have a voltage across summat, eg "you have 50V across R3, and you know there's 25A flowing through it, so R3 = V / I = 50 / 25 = 2 Ohms." </pedant>

Other than that, absolutely spot on :)
 

Reply to Resistors in Parallel Help in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi, I would genuinely appreciate some guidance. I am currently completing training for my City & Guilds 2391-52 practical, and as there is some...
Replies
19
Views
3K
Hi Everyone, New to the forum so please excuse any stupid questions which may come below. Sorry if this is long winded but I want to give a good...
Replies
18
Views
8K
Hi guys I'm a recently qualified C&G Level 2. I have my 18th edition on the way in the next few weeks. I have a CCNSG AND IPAF 3a/b card, happy...
Replies
0
Views
985

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock