Discuss Retractive press switch 2 way in the UK Electrical Forum area at ElectriciansForums.net

impish15

Trainee
Reaction score
27
Hi All,

Pretty comfortable with wiring lighting until I came across needing to install 2 way dimming with a Retractive switch. I didn’t even know there was a thing called Retractive switch. Question is how do I wire this for a 2 way dimming. More specifically which cable goes into RS on the switch?

Many thanks in advance
 
Retractive switches are used in conjunction with an impulse relay. As many retractive switches as you like can all be wired in parallel and connected to a single relay, to switch a single light or a group of light together.
Any dimming would have to be done on the load side of the relay, and wiring for that would be separate from the switch wire.
It's conceivable that a retractive switch could be combined with a dimmer, but the wiring to the impulse switch and dimmer module (again, conceivably combined into one unit) will be effectively separate.
 
You can buy 'switch dim' dimmer units with an input for retractive switches, press on/off hold to dim. This would replace the impulse relay. Some dimmers such as some Danlers models allow connection to retractive switches to allow dimming from all 2/3 etc. way positions that would allow connection if you only have 2 cores to each switch.

You can buy lights with this type of dimming feature built in too.
 
Here's an example of a dimmer module for use with retractive switches
Note the switch wire pair are separate from L, sL and N, so might be 'interesting' to retro-fit!


 

Reply to Retractive press switch 2 way in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Hopefully just a quick one, but I can't seem to find a definite answer. Will a push to break/make (ie not momentary) 2 way retractive...
Replies
7
Views
819
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
848
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
230
I've a light fitting that's controlled from a Whitecroft absence detector PIR and a wall switch. The way it works, is the Retractive wall switch...
Replies
1
Views
2K
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock