Discuss Reverse polarity at socket outlets in the UK Electrical Forum area at ElectriciansForums.net

Had some line/neutral reverse polarity today at a job instead of tripping RCD/MCB it’s just melted socket outlet how come RCD/MCB didn’t trip? RCD tested fine??
Did you check the plug? did you check the tightness of the connections in the socket outlet?, did the cables appear burnt?, reversed polarity does not normally cause any trips, any IR testing done????? lots of question I know.
 
20190910_101316.jpg
20190910_101316.jpg This was like this for 5 years and no problems......only showed up when I was doing a quick check on ring using a plug in tester
 
Is that question aimed at me......if so yes the socket was being used as normal...in fact it had an extension lead plugged in with 5 bits of equipment being used
 
I think with reverse polarity the main problem is with switching - the switch cuts out the live which in this case is the neutral so any devices plugged in would still in effect, live when the socket is switched off (potentially very dangerous)
 
Couple of years ago was testing a new school block, five classes with dado power. Four were fine but one class every socket reversed.
 
I think with reverse polarity the main problem is with switching - the switch cuts out the live which in this case is the neutral so any devices plugged in would still in effect, live when the socket is switched off (potentially very dangerous)
With socket-outlets the major issue is that the fuse in the plugtop (there's a word to annoy some!) will be in the neutral conductor rather than the line/phase conductor.

Reverse polarity in a socket-outlet should be regarded as a serious breach of the Wiring Regulations.
 

Reply to Reverse polarity at socket outlets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
576
just had a new meter fitted,tells me most sockets are faulty and not to use,all sockets apart from two show live neutral reverse. going to egypt...
Replies
9
Views
882
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
818
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock