Hey there,

Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52.

My question is I had a fault which I couldn’t find or rectify during a periodic test that I carried out yesterday (tenant property) occupied.

Circuit: Ground Floor Socket
32A Ring (r1 0.42, rn 16, r2 0.71)
R2 0.42 x 1.67 = 0.701 = Good above apart from rn!

Whipped all sockets off and checked connections at db of course. Couldn’t find anything at this point. Checked all points. Last thing was left was lifting floor boards. I couldn’t find anything in between (JB, interconnection, joint) I’ve asked tenant, unfortunately no relevant answer for an indication.

Carried out a long lead test CU - rn one leg (T&E) walked around - found dead leg from one point to the next that was giving 16ohms. Point A-B.

Split ring x2 radials (20A x 2 protective devices)

Carried out the procedural
Test R1/R2
R1/RN
Confirmed polarity….

Now getting voltage fluctuations and getting some sockets working and some aren’t due to not having 230VAC at every point on “Ground Floor Socket”

I believe there could be another dead leg or broken neutral, loose or lost.

Advice people? What would you?
How would you go about it?
 
Good approach so far.
Double check your CU connections just in case.
Sockets that aren’t working, test L to E for 230v to determine if problem is still the N.
Long lead test of all 3 conductors, also consider removing all accessories and IR test end to end.
I know this will/should give 0 but it can also occasionally “blow apart” the problem connection and make finding it easier (an old fire alarm service trick). If the test result suddenly rises, bingo!

There does come a point where re wiring a leg is the only sensible option - hopefully it won’t come to that!
 
Good approach so far.
Double check your CU connections just in case.
Sockets that aren’t working, test L to E for 230v to determine if problem is still the N.
Long lead test of all 3 conductors, also consider removing all accessories and IR test end to end.
I know this will/should give 0 but it can also occasionally “blow apart” the problem connection and make finding it easier (an old fire alarm service trick). If the test result suddenly rises, bingo!

There does come a point where re wiring a leg is the only sensible option - hopefully it won’t come to that!
Thank you bud. I’m loving this forum already being in communication with like minded individuals like yourself who can share knowledge.
 

Reply to Ring circuit fault, High RN in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
498
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock