Discuss ring circuit for a submain? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
trying to find answers in the reg book, but is there anything to say you can't install say a larger ring circuit for a sub main? to reduce volt drop / cable size etc.

Normally you would obviously install a large enough cable, but would this be acceptable , whats our thoughts?
 
trying to find answers in the reg book, but is there anything to say you can't install say a larger ring circuit for a sub main? to reduce volt drop / cable size etc.

Normally you would obviously install a large enough cable, but would this be acceptable , whats our thoughts?
Surely it would then be a parallel circuit/parallel conductors .....There are requirments for installing/designing a parallel circuit/conductors.

A brief guide to the use of parallel conductors - https://www.voltimum.co.uk/articles/brief-guide-use-parallel-conductors
 
Yes, seen plenty sub-mains cables ran in parallel. Ie it’s eaiser to install / terminate 2 x 150mm SWAs, than one big beast of 300mm2!
Only ring circuit (for sub-main) I’ve seen was in a prison, a 4 or 6mm2 ring circuit in trunking, ran round a number of cells, each had a small DB (fitted out side above the door) for the light and socket.
 

Reply to ring circuit for a submain? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
280
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock