Hi guys. Ive generally no problem going through the deign process of cable selection for a circuit to be installed, (i try keep my hand in now and then rather than just looking in the OSG) but when i look at a RFC as in appendix 15, i get a little stuck. Ib = 32A, so In = 32A breaker, take it the cable is clipped direct to avoid any correction factors in this example, so far so good. So now i find a cable Iz, from the tables in appendix 4 to carry this 32A, im looking at table 4D5. Here, i feel sure we treat this ring as two radials supplying any particular SO on the ring. So each leg now needs to be able to carry 16A, and im assuming here, that we select 2.5mm T&E because of the time current characteristics of our 32A CB?, as both 1.0 and 1.5mm sq cable can carry this load, but could become a serious hazard under fault conditions, whereas 2.5 shouldn't?!
Also, do we calculate the voltage drop over the entire length of the cable, taking it that a SO could be midway or a few inches from the origin of the circuit? and the long leg would suffer far more volt drop?
Cheers
 
The minimum cable rating for a standard RFC supplying BS1363 accessories is 20A, after correction factors have been applied.
There are a number of ways that you could use to work out VD, although it is generally accepted that if the total floor area covered by the RFC is no greater than 100m², it will be within limmits.
 
Hi guys. Ive generally no problem going through the deign process of cable selection for a circuit to be installed, (i try keep my hand in now and then rather than just looking in the OSG) but when i look at a RFC as in appendix 15, i get a little stuck. Ib = 32A, so In = 32A breaker, take it the cable is clipped direct to avoid any correction factors in this example, so far so good. So now i find a cable Iz, from the tables in appendix 4 to carry this 32A, im looking at table 4D5. Here, i feel sure we treat this ring as two radials supplying any particular SO on the ring. So each leg now needs to be able to carry 16A, and im assuming here, that we select 2.5mm T&E because of the time current characteristics of our 32A CB?, as both 1.0 and 1.5mm sq cable can carry this load, but could become a serious hazard under fault conditions, whereas 2.5 shouldn't?!
Also, do we calculate the voltage drop over the entire length of the cable, taking it that a SO could be midway or a few inches from the origin of the circuit? and the long leg would suffer far more volt drop?
Cheers


Ring final circuits should NEVER be designed/installed with a long leg as you put it. The load should always be evenly distributed (as far as humanly possible) throughout the overall rings length...
 
staggered home from the pub, more like. LOL.
 
Thanks for that spinlondon. I'm ok working out VD on a radial cicuit, but in a RFC where theres no furthest outlet as such, i get a little confused. Cant quite get my head around the VD at each outlet of a RFC, wether it differs from outlet to outlet or is the same. If r1 is the same at each SO, instinct would have me believe VD is the same at each SO. Irrespective of that, instinct also tells me to calculate VD over the entire circuit length, CU back to CU. I appreciate its accepted to be within limits if the circuit is installed according to appendix 15 and would be adjusted for any correction factors. Im sure there are more important questions. I was just curious about the details.
Cheers
 
Hi engineer54. I appreciate distributing the load in a RFC, my appollogies for exagerating a SO being so close to the CU. What i was trying to point out is that the SO's vary in distance from the CU and each other, is the VD at each SO the same, unlike a radial, A2 orA3 and would i calculate VD over the total length of cable used for the RFC, ie CU back to CU
Cheers
 
hmmm, if you do any sum on this , which i havent really a clue as never thought of it before, just the 100m area, the readings still come out more than 11.5v.........
 
HI i=p/u. Thanks for letting me know the readings dont tally either. The only way ive looked at this is as follows. I know this is rubbish, it has to be, im completly missing something, not only for a RFC, but also for the A2 and A3 radials in appendix 15. From the OSG the resistance of 2.5 T&E with 1.5 CPC is 0.01951 ohms per meter (m). Our PD is rated at 32A on the RFC and A2 radial and our V (VD) is 11.5V, so using R = V / I we have

0.01952 * m = 11.5 / 32

m = 18.41 ????

with a PD of 20A for the A3 radial

m = 29.45

i know we can construct a RFC and a A3 radial out of that much cable, but i wouldn't be able to cover an area 100m sq and 50m sq respectivly

For an A2 radial 4.0mm sq cable with 2.5cpc the resistance is 0.01202 ohms per m, so again

0.01202 * m = 11.5 / 32

m = 29.89 ?????
its beyond me. Shall just take appendix 15 as it is i suppose!

Cheers
 
im reading the big green book, or i would attack this from all angles... but i never heard anyone talking about it... i say just take appendix 15 as it is
 
Well, whos gonnan argue with einstein! I was just reading the big red book i-p/u, im still saving up for a green one. The bottom of pg 257 and the top of pg 258 sum it up i suppose. Have a look when you have time, if you havent burnt your red one already. Ive just looked at the mV/A/m values in table 4D5 and got different answers to earlier!, but according to pg 257-258 these new figures are correct.
mmmmmm????
Just don't get how they introduce VD as a necessary design element and then show standard circuits for construction in appendix 15 that fall short of their own criteria
 
I thought you calculate VD based on Ib not on In :thinking:


Edit:
Sorry, I see back in your OP that you are saying your Ib and In are the same. I just assumed that your Ib would have been lower, and that you were basing your example on a 32A CPD.

Cheers
 
Last edited by a moderator:
Hi jamesbrownlive. You're quite right that when calculating VD we use Ib, sorry if i used In above, but in this instance the(A1 A2 and A3 circuits) from appendix 15 have, Ib = In. Appendix 15 gives us the PD values for A1 A2 and A3 and we know we need Ib<=In, so the value of Ib can be equal to but no more than the PD ie 32/30A A1, 32/30A A2 and 20A A3
 
Having thought about it further, when calculating VD for an RFC you need to divide the VD by 4, because the length of the cable is halved, with twice the CSA. Hope that makes sense.
 
No the expected load at a BS1363 accessory is a maximum of 26A, though it is generally taken as being 20A.
You also appear to be forgeting to halve the figures for a RFC.
 
So if you had a 40m RFC (Just enough to cover the 100m2 floor area) with an Ib of 32A and using 2.5mm T&E, you would calcualte the VD as:

18 X 32 X 40

= 23,040

/1000

Gives you a total VD of 23.04V

Divided by 4 gives a working VD of 5.76V
 
Thanks for that jamesbrownlive. What you say is making sense to me and i understand the logic. Your answer reminds me about the fact that resistance is proportional to length and inversly proportional to CSA. Will ponder this and try get my head around it in relation to how a RFC is constructed.

With Thanks
 
Well, i wouldn't of thought so i = p/u, least i hope not. Diversity cannot be applied during the design process/cable selection process, we have to select cable size according to the full load and after considering correction factors. Diversity is not a part of cable selection
 
kk i remeberr somewhere someone did say divide by 4 now .....

what is the sum you were doing a above too work out how many meters you could get?? what did m stand for? say 11.5v divide by what = what...... i like to know things inside out.....
 
Ive used both ohms law R = V / I and used the values of mohms per meter out of table 4D5 in BS 7671.


From the OSG 2.5 T&E has a resistance of 0.01951 ohms per meter, so R = 0.01951 times m (meters) that is

R = 0.01951 * m

Ive taken V as volt drop at 11.5V and I as 32A, the rating of the PD, giving:


0.01951 * m = 11.5 / 32 ohms law


or m = (11.5 / 32)/0.0195 = 18.43m ??


Using the mV/A/m from table 4D5 of BS 7671, we have a value of 18mV, therefore

(18*32*m)/1000 = 11.5V


or m = 19.96m ??

Ive got this all wrong i know i = p/u. Think my perceptions of how a RFC handles voltage and current is off the scale!! But now ive had a thought from a post earlier.

Is from jamesbrownlive's post above, pg2, and how you both mention about dividing by 4. It would seem logical that when considering a RFC's construction, we have to consider that as a ring the CSA is doubled and the length effectivly halved, which would reduce the resistance to 1/4 of its standard value of 0.0195 ohms per m, in this case that would become 0.004875 ohms per m. Recalculating we have:

0.004875 * m = 11.5 / 32

m = 73.7m
which now seems ample length of cable to construct an A1 ring

What you think?
 
Last edited by a moderator:
Of course diversity is used during the design process/cable selection.
When else would you use it?
It would be a bit pointless applying it after you have designed and installed the circuit.
 
Widler has a good drawing for this. I think it’s in one of the sticky’s. It’s easy when it’s drawn out. (I’ve got to get this bloody PC sorted out so I can post drawings!)
 
open the window tony and launch it... im sure the forum could sponsor you new 1 as you a classy/smart contribuiting member.. tho grumpy
 
Tried both, they both work until it gets to this site, and then I’m back to “mobile crap” screen. PLEASE someone HELP it doing my bloody head in ! ! ! ! !
 
Sounds like your computer thinks it is a mobile phone, so the forum is sending you to the mobile site or vice versa.
Unfortunately I do not know how the forum does that (client or server) so can't help.
Usual things of clearing caches, directly typing the forum address in the address bar not using links/favorites. but you have probably tried all that. Make sure there are no spurious m's in the web address you go to.
Good luck
 
Ive used both ohms law R = V / I and used the values of mohms per meter out of table 4D5 in BS 7671.


From the OSG 2.5 T&E has a resistance of 0.01951 ohms per meter, so R = 0.01951 times m (meters) that is

R = 0.01951 * m

Ive taken V as volt drop at 11.5V and I as 32A, the rating of the PD, giving:


0.01951 * m = 11.5 / 32 ohms law


or m = (11.5 / 32)/0.0195 = 18.43m ??


Using the mV/A/m from table 4D5 of BS 7671, we have a value of 18mV, therefore

(18*32*m)/1000 = 11.5V


or m = 19.96m ??

Ive got this all wrong i know i = p/u. Think my perceptions of how a RFC handles voltage and current is off the scale!! But now ive had a thought from a post earlier.

Is from jamesbrownlive's post above, pg2, and how you both mention about dividing by 4. It would seem logical that when considering a RFC's construction, we have to consider that as a ring the CSA is doubled and the length effectivly halved, which would reduce the resistance to 1/4 of its standard value of 0.0195 ohms per m, in this case that would become 0.004875 ohms per m. Recalculating we have:

0.004875 * m = 11.5 / 32

m = 73.7m
which now seems ample length of cable to construct an A1 ring

What you think?

I think your not far off, you need to make a further consideration to load distribution and conductor temperature and your there.

Regards Chris
 
I use an (Ib) of 26A when calculating for an A1 RFC which would gives a maximum length of 98M.

It can be engineered further but I prefer to err on the side of caution with 26A and (Ct) of 1.
 
Hi spinlondon, i never been taught to use diversity with cable selection. That doing so is is a definite no no. Diversity is applied to maximum demand to give a practical/realistic expectation of the current being drawn off he supply and hence through the service fuse at any one time.
 
Cheers chris. Im trying to get my head around load distribution and the calculations.
Get what you say about conductor temperature.
I've done the calculation without any correction and method C to keep things as simple as possible
 
Hi spinlondon, i never been taught to use diversity with cable selection. That doing so is is a definite no no. Diversity is applied to maximum demand to give a practical/realistic expectation of the current being drawn off he supply and hence through the service fuse at any one time.
Consider then a RFC with 10 socket-outlets.
What CSA of cable would your method indicate, and what rating of CPD would be required?
 
That is how I work out the length and volt drop in a Ring.

Length

2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}

so if you have a measured value of say

r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m

Volt Drop

Divide the length by 4 = 19.57 x 18 x 26/ 1000 = 9.16v

Bs 7671 pg 258, 6.1 correction for operating temp.

This calculation give you a ct of .923, x 9.16 = 8.45v

or

4 x 8.45v x 1000/26/18 = 72.22 / .923 = 78.24m

It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,

average = (32 + 20)/2 = 26 which is the value that Lenny posted.
 
Last edited:
Hi lenny, im with i = p/u. Can we see you full calc
Cheers

Ok, VD will limit the length of your RFC before any other factor. So if we use our max permitted VD of 11.5V in our calc for finding the max permissable length we 'should' arrive at a value within the 5% tolerance.


So (4 x 11.5 x 1000)/(Ib x mV/A/M x Ct) = max permissable length.

= (4 x 11.5 1000)/(26 x 18 x 1) = 98.29M.


As I said it can be engineered further to give a longer length but I personally use the above.
 
Last edited by a moderator:
Cheers for your help spinlondon, things are getting clearer. Have always taken appendix 15 as is, with no explanation of the design behind these circuits. Radial are fine, the ring threw me, so thanks for your help in this matter
esc
 
nice sums malcom, but can you say lets say you have values for r1 r2 rn... if you designing or longest possible
That is how I work out the length and volt drop in a Ring.

Length

2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}

so if you have a measured value of say

r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m

Volt Drop

Divide the length by 4 = 19.57 x 18 x 26/ 1000 = 9.16v

Bs 7671 pg 258, 6.1 correction for operating temp.

This calculation give you a ct of .923, x 9.16 = 8.45v

or

4 x 8.45v x 1000/26/18 = 72.22 / .923 = 78.24m

It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,

average = (32 + 20)/2 = 26 which is the value that Lenny posted.
 

Reply to ring design and voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
995
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
961
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock