Discuss Ring final circuit question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
3
When you do the continuity test on a ring final circuit and you have to connect L1 to N2 and vice versa, this assumes you know which L cable is the incoming or outgoing.

I understand that if you connect L1 to N1 and vice versa the ohm readings rise then fall as you go round the ring circuit. Why is this? I can't explain this to a friend who asked.

If the connections are done correctly the readings stay the same as you go round.

Thanks
 
Hi Peter, are you a trainee ?

The reason is that in cross connecting the line and neutral conductors you are creating a closed loop through all the live conductors. When you measure at the socket you are measuring the same loop at each point and so should get roughly the same reading.
 
Hi
Yes...in training.

I understand why they should be the same reading.

but what happens if you connect L1 to N1 and cross connect L2 to N2?

the readings change then don't they? Why is this?

Have a think about what you are actually measuring with the cables connected in both situations. Sorry but I'm away back to work now.

If you ask a moderator there is a great training sub forum here you can apply for entry to.
 
I Sussed it.

if you do it the correct way L1 to N2 and L2 to N1 you effectively create two identical loops. Taking a reading at any socket effectively measures the resistance across two loops of equal length in parallel.
So using the equation for resistances in parallel the resistance will be the same each time.

if you connect L1 to N1 and L2 to N2 you lose the equal loop sizes at each socket. Thus when measuring the resistance across two unequal length loops and the total resistance will change becoming higher the further you go round the ring and then falling again.

Makes sense now I have drawn it out more simply and thought of each leg of the ring as a resistor.
 

Reply to Ring final circuit question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
Hi all, I had a fault on site today I've not encountered before. if anyone could shed some light on a similar fault they may have encountered...
Replies
9
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
996
I am not a qualified electrician, I was employed as an electrician after my MoD electronics apprenticeship but that was 30 odd years ago. So I...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock