Discuss Ring main continuity test in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 112675

I'm not sure if this is a reasonable question or so stupid it shouldn't be asked. If the latter than I apologise and hope I don't get too much negativity back.

So I want to perform the test Continuity of ring final conductors on an existing ring main. Because I'm lazy and its dark outside, could I do this whilst the rest of the CU is live?

My thoughts are to pull the MCB for that circuit and pull the earth cables from the bar out too. Then for neutral, first check the neutral bar in the CU is at the same potential as earth by using a cheap multi meter to check for continuity to earth. If good, then remove the neutrals for that circuit.

Then with both cables removed, carry out the testing as per normal.
 
Do you know the different steps for checking continuity of an RFC?

Have you got the means to carry out safe isolation ? And the said steps?

Do you know how to interpret the results and what you’re looking for, or trying to confirm while carrying out the tests?
 
Hi - imagine you were changing a broken outlet on that RFC. After safe isolation you would have both ends of the ring available, all 6 conductors :) .

Hi. Thanks for that thought. But if you did your testing there, the neutral and earth would still be connected to the earth and neutral bars in the CU so the test wouldn't be valid would it ?

Why would you want to use a cheap multi meter?!!

If you don't need to test very low resistance accurately then why not use one? Obviously for the ring main continuity test itself I will use my multifunction tester.

In general, other than Wilko's interesting post I don't seem to have gained much by posing the question and I should have realised that. Certainly if a professional electrician working on installations every day, I can see why you would never entertain not even a crumb of risk. But in your own house with wifes and babies to worry about.....maybe you still wouldn't but I suppose even if you would you wouldn't suggest its OK on a forum like this.

I'm leaning towards doing it properly with the cu switch in the off position.
 
A confident/competent electrician would almost certainly be able to carry this out without the consumer unit being isolated, this would be their choice but if the option is there to isolate it then this is the suggested option. In your case isolate and ensure it is dead using a proprietary test device.
 
using a cheap multi meter to check for continuity [from neutral] to earth

This may give you an invalid reading. Although there should be continuity, the resistance to the point at which N & E connect is not zero, especially on a TN-S supply where that point is at the local substation down the road. Load current passing through the resistance of the neutral cable causes voltage drop, which is then superimposed on the meter's measurement voltage. Meters and MFTs are designed to reject minor line frequency interference, but adding a few volts of 50Hz plus all the 3rd harmonic and hash to the meter's few hundred mV of measurement can throw it completely out. Continuity tests only work properly on de-energised conductors.

Anyway, what good is knowing that there is continuity now, if you knock the main switch and the neutral breaks first, or something goes high-resistance while you are putting pressure on the neutral bar, etc.

Please isolate it.
 
But in your own house with wifes and babies to worry about.....maybe you still wouldn't but I suppose even if you would you wouldn't suggest its OK on a forum like this.

That is exactly the reason you shouldn't put yourself at risk, your wife and children. Is it worth risking your wife becoming a widow and your children growing up without a father?
 
Hi. Thanks for that thought. But if you did your testing there, the neutral and earth would still be connected to the earth and neutral bars in the CU so the test wouldn't be valid would it ?
Source URL: Ring main continuity test - https://www.electriciansforums.net/threads/ring-main-continuity-test.181316/#post-1594305

I think what was being suggested was, isolate the circuit, then perform your continuity testing at an outlet on the circuit, therefore avoiding the need to take the cover off & go poking about in a live board.
But if you're testing at an outlet, and you remove the conductors from the earth and neutral bars your not going to have continuity are you?!! Sorry if this is negative but this is pretty basic stuff for someone who claims to own a multifunction tester.
 
Last edited:
Hi. Thanks for that thought. But if you did your testing there, the neutral and earth would still be connected to the earth and neutral bars in the CU so the test wouldn't be valid would it ?
Source URL: Ring main continuity test - https://www.electriciansforums.net/threads/ring-main-continuity-test.181316/#post-1594305

I think what was being suggested was, isolate the circuit, then perform your continuity testing at an outlet on the circuit, therefore avoiding the need to take the cover off & go poking about in a live board.
But if you're testing at an outlet, and you remove the conductors from the earth and neutral bars your not going to have continuity are you?!! ion tester.
Sorry if this is negative but this is pretty basic stuff for someone who claims to own a multifunction
Hi. Thanks for that thought. But if you did your testing there, the neutral and earth would still be connected to the earth and neutral bars in the CU so the test wouldn't be valid would it ?
Source URL: Ring main continuity test - https://www.electriciansforums.net/threads/ring-main-continuity-test.181316/#post-1594305

I think what was being suggested was, isolate the circuit, then perform your continuity testing at an outlet on the circuit, therefore avoiding the need to take the cover off & go poking about in a live board.
But if you're testing at an outlet, and you remove the conductors from the earth and neutral bars your not going to have continuity are you?!! Sorry if this is negative but this is pretty basic stuff for someone who claims to own a multifunction tester.

Hey,steady on...i've got a torch...but i'm not a midwife ;)
 
Hi. Thanks for that thought. But if you did your testing there, the neutral and earth would still be connected to the earth and neutral bars in the CU so the test wouldn't be valid would it ?
Source URL: Ring main continuity test - https://www.electriciansforums.net/threads/ring-main-continuity-test.181316/#post-1594305

I think what was being suggested was, isolate the circuit, then perform your continuity testing at an outlet on the circuit, therefore avoiding the need to take the cover off & go poking about in a live board.
But if you're testing at an outlet, and you remove the conductors from the earth and neutral bars your not going to have continuity are you?!! Sorry if this is negative but this is pretty basic stuff for someone who claims to own a multifunction tester.

Yes I realised that and what I was saying was if you do that your circuit is not fully isolated because it is connected to the neutrals and earths of other circuits in the CU. I can see though that you should be able to obtain a consistent set of results doing that and it does seem to be an interesting and practical way of doing it. Still I'd rather do it exactly as proscribed and shall isolate the board before fully isolating the circuit under test.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.

The 2 most likely reasons for the discrepancy from the x1.666 ratio are:
  • The cable is over 40 years old, and still had a 1mm earth with the 2.5mm live cores.
  • There is at least one case of a poor connection. Quite often you will find the result improves incrementally after reterminating the earths in each socket.
BTW, if this is the main ring circuit for the house, it appears to be quite small, and may indicate that a number of sockets (usually the downstairs ones) have been wired as spurs from a small ring. This is not a major problem, but isn't ideal for any modifications, and usually indicates an old installation.
 
Since it was so quick to do, I decided to try Wilko's kind suggestion. I've only done the easy first part partly because I know it is a ring (its in my house and I've seen it) and partly because I just wanted a sanity check before doing a load of other work and then a final test.

Anyway, the numbers around the ring in ohms were:
L 0.18
N 0.17
E 0.41

This is 2.5mm twin and earth.

That last reading was higher than I would expect since I think it should be around 0.3 but not sure if its anything to worry about. Perhaps my earthing terminals are not as tight as the others.
Your cpc will have higher resistance because the conductor is smaller.
 
Thanks very much to the majority who have given me good advice on this thread. I have nevertheless learned my lesson that talking about working live esp for a DIYer is going to annoy one or two so I shan't do that again. I do deliberately use "DIY" terms such as earth instead of CPC etc so that it is very clear I am a DIYer just in case you miss the DIY badge of shame above all my posts.

I have a lot of respect for those in many trades including electricians. DIY "bodgers" have had a terrible press of recent years in many cases with justification. The problem people face is that when you call someone out to do some work, how do you know they've done a good job? Most people are honest and will do good work even when the work is out of site but some will not. If Mrs Miggins sees her shiny new sockets & switches and they all seem to work ok how is she going to know if the installation is dangerous ? That is my motivation to DIY.

Your cpc will have higher resistance because the conductor is smaller.

Yes but not that high. It should be 2.5/1.5=1.6667 times higher but is much closer to 2.5/1 which as some have kindly suggested might indicate a 1mm conductor somewhere in the ring.

That did worry me for a short while because much of that ring was installed perhaps 20-30 years ago but I did compare the earth with a known 1mm earth and a known 1.5mm earth and it is definitely 1.5mm.

I finally resolved the issue though. Whilst the raw numbers pointed to a 1mm somewhere, I have less faith in my conductor termination skills than some of you do. So I removed all the newly added sockets one by one and connected the earths together using a wago connector (which even I can get right). As I did so I took fresh readings and sure enough the earth resistance around the ring started to come down. When I'd change all 6 I was down to 0.32 Ohms which in conjunction with the other numbers is much more consistent with a 1.5mm earth. THe problem was I simply wasn't terminating well so I went back to the drawing board, watched a couple of John Ward videos, and I plan to start looping the ends of the conductors back on themselves to fill the connector.

Thanks once again to most all of you who helped me with this.
 

Reply to Ring main continuity test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
310
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock