sparky928

Had a call this Morning that her rcd keeps tripping.


So i went round there First of all unplugged everything still tripping. Done a few tests L-E N-E L-N and end to end test all came back as 0 mohms.

So i Separated the legs at both the board and the sockets found the fault leg.

Reconnected the good leg got a good part of the sockets working.
So i went upstairs as the cables are coming down to the sockets and the room above is the bathroom with vinyl flooring. She didnt want me to the lift the floor up without speaking to her husband.
.
And then the customer tells me that a few months back they had a leak in the bathroom.

i was thinking water probably got in the junction box.

By why didnt it trip a few months back?
 
Welcome to the Forum Sparky928 :)

In reply - Your guess is as good as our until you get to the joint or damaged cable we all can only guess.
 
I would find the joist run direction and take a board up in an adjacent room to see if you can see across under the bathroom.. the actual fault may not be under the bathroom, it may just seem its likely to be there. Also see if the bath panel comes off and you have access under the floor beneath the bath.
 

Reply to Ring Main fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
483
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
472
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
286

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock