Search the forum,

Discuss Ring main. in the UK Electrical Forum area at ElectriciansForums.net

Soi disant,
Nice diagrams and well put.
Yes I like it.

Ok the point I was making.

With a bridge that makes a ring final become a "fig 8" it means that we tend to lose control of which leg gets more of the current x usage factor. A I said we don`t usually go to great lengths do control this however we do a quick approx to see if it looks badly slanted in favour of one leg or the other and then perhaps re-adjust our plan in order to balance it up a bit. This helps with heating issues and therefore aging of cables and helps reduce overloads of cables.

I`m not suggesting that fig 8 or indeed that lovely matrix thingy you drew for use is going to cause fires and threaten life everytime it`s used, far from it.

It is complicated enough to make predictions even with a well designed ring final and the fig 8/matrix complicates this further.
In reality, much of the time, no great problems should arise from it and if every ring final was done that way I don`t think we`d find streets littered with dead bodies.

However, of all the differing combinations of power drawn at various points around the ring then this arrangement is far more difficult to follow, calculate and therefore enjoy the most reasonable aspects of ring benefits as originally conceived for current flow considerations. It also makes it difficut to test properly too (OK that one can be said, to a degree, about the 2, 3, 4, umpteen rings on one ring final circuit too!)
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responses
 
If I start with this:

View attachment 84116

and add a loop like this:

View attachment 84117

or if I start with this:

View attachment 84118

and add a link across the middle to end up with the same figure of 8, which cable(s) become at risk of being overloaded that would not if I'd done this:

View attachment 84122

?


The more paths there are for current to flow to each point of loading the less flows in any given one, not more.

Ignoring the practical realities of actually wiring it, a "full mesh" topology of interconnections

View attachment 84124

would minimise the current flowing in every single cable (apart, obv, from the ones from the OPD to the "first" and "last" sockets, but those cables are never affected by any interconnection topology anyway).

And the more connections you have the harder it becomes to turn the circuit into radials, or to create multi-socket branches, by cutting connections.
youneed to get out more. don't the pubs open soon?
 
youneed to get out more. don't the pubs open soon?
If you are referring to me Tel, then nothing gets up my snout more than Wannbee's quoting something they know little or nothing about post ban waiting, still no one likes the truth these days do they?
 
youneed to get out more. don't the pubs open soon?
LOL.

yes it is a ring final cct not a ring main.

You might find a ring main in the street.

You might find a ring main at a power station etc (although not really the type you find in the street.

A ring final in installtions - domestic or otherwise
 
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responses

Pete, I think you might have quoted the wrong person.
 
Pete, I think you might have quoted the wrong person.
probably did in my state of mind, going to give up for a while far to much goin on in my bonce at the moment might even have to resign?
 
If you are referring to me Tel, then nothing gets up my snout more than Wannbee's quoting something they know little or nothing about post ban waiting, still no one likes the truth these days do they?
i was referring to the poster who drew all those figure 8 etc. circuits.
 
Pete, I think you might have quoted the wrong person.

probably did in my state of mind
It happens. A few times (not here) in the past I've had "discussions and debates" (ahem...) lasting multiple posts where I've misattributed what had been said. The arguments over what had been said were valid, but with the wrong person.

Worse things happen at sea.
 
Actually, just to be a bit naughty - what is unsafe about a large number of radials, each one having not more than one twin socket and all connected by say one 32A MCB. Not actually unsafe proving the joints are reliable both electrically and mechanically and all volt drop and Zs are catered for.
I wouldn`t like to see it but it would not cause piles of dead bodies to litter the place.
Bring back (and uprate) the octopus....
 
Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??

If so does this meet the current regs.

TIA.
It is actually 1 RFC with an intermediate connection. And the answer is No you can not have it and this is the specific fault that we are looking for when conducting the cross connection RFC test. It just happens to be in a place visible.
 
Some how the good old ring thread has bounced back again.
Ring final circuits are often found in homes and a few other properties. Ring mains are not.
Ring mains are of two main types.
You might find a ring main underground feeding a housing estate from a substation. This reduces voltage drop. If it`s calculated as a full size radial then it means it may be possible to disconnect a portion for repairs etc but leave the remainder energised.

You might find a ring main at a power station. Several generators (or a transformer fed from a distant part of the grid). Wired, full size, as a ring, with isolators between each connection, allows a generator or an adjacent group of generators to be taken out of service for replacement/repairs/upgrades whilst the rest are still running.

A spur is something similar to a spur on a railway track. A spur on a ring is often a piece of cable branching from the ring final and feeding a socket or sockets. This spur might be fused down using a switched or unswitched fused connection unit.
Unfortunately a FCU or SFCU is often referred to, incorrectly as a spur. Unfortunately a ring final is often referred to, incorrectly, as a ring main. Much the same as a Line conductor is often referred to as Live, whereas both Line conductors and N conductors are correctly referred to as Live.

If we have a consumer unit that has a number of radial circuits and say a couple of ring final circuits on it then say we redesign it for some reason an put the two rings on one fuseway (to free up a fuseway to add another circuit for example) then it now becomes two rings but only one circuit. Perhaps not very elegant but still perfectly correct so far as our regs are concerned - providing that all other considerations for a ring final circuit are net (floorspace served, overloading etc etc).

Someone did suggest disconnecting one end of each such ring from the fuseway and connecting them together to form a longer ring. All that would do would be to increase volt drop and would be of no benefit.

You could take two or more radial circuits and connect them together in one fuseway. Again that becomes one circuit.

You could make a ring final circuit with a spur (one twin socket) at the origin. You could later disconnect the ring from it therefore leaving just the radial. On a 30/32A overcurrent protective device. Therefore you would have a 2.5/1.5 radial circuit containing one twin socket. This would not make it suddenly become dangerous because you have disconnected the ring from it.

The On Site Guide gives us examples of standard circuit considerations but that does not mean you can not design non-standard circuits providing you use sound engineering judgement and apply the regs to do something as little different. It might look a bit odd at first glance but that in itself does not make it wrong.

I have heard some say that ring finals are old hat and we don`t do them anymore. Well they might be a bit old hat, they are peculiar to the UK but have stood the test of time. They still can (and often are) done these days and are still in the OSG and in the informative parts of the Regs Books. They have some advantages over radials but also some disadvantages over radials too.
 
Cos you posted in the thread. Post #335.
Ah so I did. There was also another post at #320. Must have been a busy week.
Just a note. The only reason why two ring final circuits end up paralleled up into one mcb/fuse terminal is likely to be a short term temporary measure because there are no spare fuse ways. The Dist. Board is about to upgraded.....
 
Ah so I did. There was also another post at #320. Must have been a busy week.
Just a note. The only reason why two ring final circuits end up paralleled up into one mcb/fuse terminal is likely to be a short term temporary measure because there are no spare fuse ways. The Dist. Board is about to upgraded.....
As long as they are marked up. Easy to find, I know............ but not for some, maybe?😉
 
Oh of course, the trainee needs to establish himself as a pedant as soon as possible after all that is what all electricians aspire too.
Does anyone really care if the ring main disappears into the either, to be replaced by dare I say it the R.......
And while we're on the subject, it's 'ether'
 
New posts

Reply to Ring main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
251
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
951
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
443
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
269

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top