Reaction score
1
Hi, i swapped a cu yesterday and now the combi boiler wont operate off the wireless room stat. it works on advance on the boiler on still gives hot water. I did I/R reading between L-e N-E so can't be that, and rcd auto test in the board. The only thing i did was ZS from fused spur. I have tried paring the roomstat again and changing the battery's but it still wont work.
 
Cant see how a CU change would stop the stat from working, and neither would a Zs test. It sounds as if you have just been unlucky and the stat chose to die at the same time as you changed the CU. Fit a new one and see what happens.

Cheers.......Howard
 
Do it work before you touched anything ?

I don't take chances with IR Tests unless I disconnect items like combi's which house electronic components. I would phone boiler technical for advice.
 
Yes it worked fine, Didn't disconnect it tho, but was careful only doing I/R test L-E, N-E. The only thing that could have caused any damage? was rcd auto test from out going on mcb and earth bar. Never had a problem before tho.
 
Believe it or not, i did a CU swap yesterday and the client phoned yesterday eve saying the CH progammer had no lights on it.

Got down there and yep, no lights.

Turned out to be U/S ( it was over 20 yrs old), so replaced and now all working fine.

i have no idea why it went and usual precautions were taken when testing...
 
next time do an IR test at 250 and not 500 that might help. or connect L and N together in a connector block and do IR test between that terminal and earth at 500. this wont damage electronics.
 

Reply to Roomstat wont work after board change in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock