Discuss Routing of meter tails in the UK Electrical Forum area at ElectriciansForums.net

I can't see what fitting 16mm twin and earth would help? Especially as the cpc size would be too small
The cpc in the 16 mm would only be the distribution circuit cpc and not the main earthing conductor (that’s if a suitable sized conductor will be installed at the origin) so depending on the zs at the consumer unit it will most likely be satisfactory for use as a cpc only.
Tho If your bonding conductors are connected at the consumer unit then it’s another story....
 
Going away from who has the biggest core...

Is the OP concerned about the vulnerability of the animal wagging parts,where they have been installed?

I get the feeling,this may be his concern.
 
If it is a TN system an rcd is
Going away from who has the biggest core...

Is the OP concerned about the vulnerability of the animal wagging parts,where they have been installed?

I get the feeling,this may be his concern.
sorry for the late reply, yes this is a concern. It is a TN system NOT TT so as pointed out earlier in the thread RCD protection not required.
 
Animal wagging? I've checked the regs and I can't find this.
 
Which goes back to the dilemma of you first energising part of an installation, someone else has installed. Not trying to be clever, just wonder how you would cover yourself on the EIC, not having inspected after installation.

Must be a solution, as this happens more than not?
 
Which goes back to the dilemma of you first energising part of an installation, someone else has installed. Not trying to be clever, just wonder how you would cover yourself on the EIC, not having inspected after installation.

Must be a solution, as this happens more than not?
Fully agree and as mentioned if it wasnt an install previously started by another electrician i trust i would not have taken the job. I guess im more concerned about the use of the double insulated meter tails. Althought they are ran together and at a suitable depth ( 50mm from floor and ceiling ) i still worry that either conductor could become damaged and the fault not clear, the use of a T&E or SWA would surley reduce this with all conductors being enclosed together.
 
Which goes back to the dilemma of you first energising part of an installation, someone else has installed. Not trying to be clever, just wonder how you would cover yourself on the EIC, not having inspected after installation.

Must be a solution, as this happens more than not?
Fully agree and as mentioned if it wasnt an install previously started by another electrician i trust i would not have taken the job. I guess im more concerned because of the cable
I still don't see how T&E would be an improvement??
wouldnt you have more chance of hitting multiple conductors in a T&E, say with a nail or screw and in turn creating a short circuit causing my OCPD to operate. The way that the cables are installed shouldnt give rise to this happening, but whats stopping Mr Builder sending a 3” screw into a floorboard?
 
You cant rely on t&e to perform like that.

And as long as the cables are correctly installed then screws aren't a problem. You might as well say what if he uses 6 inch nails.
 

Reply to Routing of meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
411
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
831
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
895
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock