I've a double socket in the loft running off a spur from a bedroom socket.

I'd love to add lighting into the loft, and wondering if I can run a socket radial and lights off the spur using a junction box and 2 fused connection units?

Please see the attached diagram for a description of what I'm proposing. Please can you let me know if this is possible?

Diagram.png

Many thanks,

Edward
 
Put your 3 amp FCU after the last double socket. This will comply with the current regulations.

With your drawing there's next to no chance of overloading the cable but you never know what will happen in the future.
 
In a word no. You would need to replace the point marked ‘JB’ with an FCU, then you could carry on with what you propose.

It’s not something a DIY’er should do IMO. You’ll need some appropriate test equipment, and probably a better design, in any case.
 
Welcome to the forum mate.
Does the circuit you are proposing to alter have RCD protection?
 
Welcome to the forum mate.
Does the circuit you are proposing to alter have RCD protection?

Yeah, it's the top floor sockets circuit, terminating in the consumer unit with an RCD.
[automerge]1569351259[/automerge]
Thanks for your help everyone. Would something like this be better?

Diagram v2.png
Unfortunately the last double socket there is difficult to get another cable fed to, so would like to have that at the end of the circuit/radial.

Many thanks,

Edward
 
Last edited:
  • Like
Reactions: DPG
That’ll be fine.
 
How do you mean please? Please could you elaborate? Thanks

The plan as drawn is compliant with the requirements for ring final circuits, however there is not enough detail to know whether it complies with all other relevant regulations.
 
The last diagram is fine, but you could omit the light switch and replace the FCU with a switched version.

Also be sure that everything in the attic is off the load side of the 13A fuse
 

Reply to Running 2 radials off a spur. Is this possible? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, apologies for the basic question In a radial circuit, is it permissable to spur off the supply side of an existing fused connection unit...
Replies
1
Views
369
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
681
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
408
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock