Discuss Running a 4 gang off a spur in the DIY Electrical Advice area at ElectriciansForums.net

CrazeUK

DIY
Reaction score
0
Hi all.

I have an area of the kitchen with no work surface and no electric supply. I want to make this area usable and move the coffee machine (1kw, assuming 4.5amps) and baby steriliser (600w assuming 3amps) to that area without making huge modifications to the electrics.

The current kitchen ring is behind tiles.

The closest supplies are a washing machine (assuming 2.2kw / 10amps) socket (single, I assume is a spur) and the boiler.

Questions:
1. can I run a 4 gang socket from the washing machine to power both the washing machine, coffee machine and steriliser?
2. Can I swap the single from the washing machine to a double?

Thanks in advance.
 
Yes, you can change the single to a double, but try not to use another high power appliance on the socket at the same time.

Running these extra appliances off a four-way extension lead will be fine as the lead is protected by a 13A fuse in the plug, but again, be careful to what’s all running off it at the same time.

Buy a good quality extension lead with only enough flex as you need on it.
 
Thanks for the response. Will definitely consider that.

Also the washing machine is protected by the fuse on its cable and from a kitchen wall switch set that has all then individual appliances marked.

As an alternative, could I run it from the boiler supply (where the boiler fuse is) it is protected by the RCD?
 

Reply to Running a 4 gang off a spur in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hello there, we are wanting two new double sockets in our kitchen, one will be below counter to accommodate gas hob and ovens ignition plugs...
Replies
1
Views
1K
I'm revamping the kitchen electrics, 1980's property. Majority of the sockets have a couple of cables going in/out of them, with the only...
Replies
4
Views
877
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...
Replies
3
Views
1K
Hello. I'm in the UK, and have some questions/concerns about my kitchen set up. So the fuse box has 4 breakers/circuits for the kitchen (the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock