Discuss Running Neutral Wire from consumer unit to Ground henley block in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
In the UK, It is said that the neutral wire is connected to ground/earth wire along the way back to the substation.

Ive inherited a setup where the incoming SWA neutral wire is hard to join/reconnect to as the previous electrician hasn't used a henley block due to limited space... therefore the neutral wire is fixed from SWA entry to point B, with no busbar/henley blocks

In this situation, I am wondering what the problem would be to run my Neutral cable from my consumer unit directly to the earth henley block?

My reasoning is that the Neutral wire connects to ground at some point further down the line anyway, so whats the problem?
 
This is a job that you should be asking an electrician to quote for.
it may also need the services of your electrical supplier to fit an isolator.

what you are suggesting is not allowed and potentially dangerous.
 
This is a job that you should be asking an electrician to quote for.
it may also need the services of your electrical supplier to fit an isolator.

what you are suggesting is not allowed and potentially dangerous.

Hi James, I understand the regulatory side of it, However Im asking the question based on the actual science/physics behind it all, is it fine to do, if not, why?
 
To elaborate... a protective earth conductor is only supposed to be used to maintain an equipotential on exposed metalwork, not to carry significant current unless there is a fault. A neutral is the opposite - it's allowed to carry current but mustn't be connected to anything exposed, in case it breaks or goes high-resistance in which case the exposed parts become live. The two functions, PE and N, are only allowed to be combined into a PEN where the nature of the cables and the work carried out on them makes them unlikely to become high-resistance or open-circuit. This means that in the UK, it is restricted to the DNO's equipment and a combined PEN is not generally allowed in the consumer's installation because there's too much risk of it being wrongly disconnected.

By connecting your neutral to the earth block you would be converting the supplier's earth into a PEN which would possibly work, but is forbidden by BS7671, by the conditions of the DNO who work to the ESQCR, and might nonetheless overheat and fail dangerously because the CSA might be smaller than that of the proper neutral.

In some locations, e.g. the USA, the procedure is different and the neutral and earth are connected together (they call it 'bonded' which has a different meaning in the USA) in the consumer unit, not the DNO's equipment. But in that case it is the earth using the neutral, not the other way round, so you can be assured that it will handle the full current which a UK supplier's earth might not.
 

Reply to Running Neutral Wire from consumer unit to Ground henley block in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
739
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
638
I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3...
Replies
4
Views
933
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock