Discuss Safe Isolation of a 16/32a socket in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi, after some discussion with electricians, does removing a 16A or 32A socket constitute safe isolation? I understand that removing the socket completes an isolation, but for me, additional measures should be included, either placing a lock around the plug to prevent it from being placed back into the socket or securing the socket with a lock. The socket outlets are integrated within a test panel.
 
So you’re talking about isolation of the equipment on the plug, not the socket itself?

If it’s within a panel, then only trained persons should be working on it, so I don’t think any additional procedures need to be used. Just unplugging it under the control of the persons doing the maintenance or repair of that equipment.

Some sockets do come with a rotary isolator before it, which can be locked off, or use an MCB toggle lock.
 
Hi, after some discussion with electricians, does removing a 16A or 32A socket constitute safe isolation? I understand that removing the socket completes an isolation, but for me, additional measures should be included, either placing a lock around the plug to prevent it from being placed back into the socket or securing the socket with a lock. The socket outlets are integrated within a test panel.
Hi Dave, I am a little confused, what do you mean removing a socket and does it constitute safe isolation? are you talking about a commando plug ? or a socket? sorry for sounding a bit daft but I just feel confused by your post and would be sure if clarified I and others on here could help
 
I’m assuming the question is better written as removing the downstream plug from a 16/32 Commando (ceeform) socket. If so, then ask yourself why wouldn’t it?!

Unplug your kettle in the kitchen and then try to use it - I’d pretty much wager that you’ll discover that’s the very pinnacle of isolation.
 
if the scenario is that you have a long lead with a 16 amp plug on it supplying say a porta cabin and just by unplugging it you have provide safe isolation so you can work on the other end, 50 meters away I would say this is not safe isolation as any tom dick or harry could plug it back in, if the socket supplys an appliance and you have control of the plug then yes unplugging it would be safe isolation. Just to add most switched interlock sockets have the option to fit a lock in the switch in the off position.
 
If it's a plug on an appliance then yes as you've removed its sole source of power (assuming no battery/capacitor backups.

If you mean removing a ceeform socket for a ring/Radial then simply removing the socket won't do. You need to do something with the (now) loose conductors (Disconnection of branch and termination into a suitable enclosure (wagos and a wago box. If the whole Radial is to be removed (assuming it's a multi socket arrangement, then the same still applies; disconnection is only half the job.

You can get lockout devices for ceeform plugs and sockets (assuming disconnection is for maintainance)
 

Reply to Safe Isolation of a 16/32a socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
599
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock