Hello
I am new on this website and first want to say hello to everyone. We moved to a house with old night storage heaters. We had to replace one in our bedroom this winter. The new electric radiator is 1,1kw with a plug. Night storage were hard wired 2,5mm cable with 16a mcb on night economy 7 busbar. The cable was connected to a day busbar. Hard wire was replaced with 13a socket. Now we think to replace night storage in second bedroom. But there is no 13a sockets near and no room for another mcb on day busbar. In Europe is not recommended to have two radial lines from one mcb, but not forbidden if both same size. Is it legal here to have one mcb for two 3 core 2,5m cables with 13a sockets at the end?
 
The UK regulations on wiring are a bit different to the EU and elsewhere due to the use of fused plugs. So we do not have any specific limit on how many sockets you connect to a cable providing the cable is adequately protected from overload by the MCB.

But the fact you can have many sockets does not mean it is necessarily a good idea!

Typically here we have a 32A MCB feeding either a 4mm radial, or a 2.5mm "ring final circuit" for the various sockets. The arguments for ring versus radial go on and on so I won't even start that discussion here, but just to say either of those would normally cover multiple rooms to around 75-100m^2 total area.

The safest option would be to get an electrician in to add the extra socket. If the cable is 2.5mm and not too much thermal insulation on its route they might decide to change the MCB to a 20A one which better serves several outlets.

A final note is socket outlets today should have RCD protection. Your existing distribution board may well have that, but it is something to check before deciding what to do.
 
The UK regulations on wiring are a bit different to the EU and elsewhere due to the use of fused plugs. So we do not have any specific limit on how many sockets you connect to a cable providing the cable is adequately protected from overload by the MCB.

But the fact you can have many sockets does not mean it is necessarily a good idea!

Typically here we have a 32A MCB feeding either a 4mm radial, or a 2.5mm "ring final circuit" for the various sockets. The arguments for ring versus radial go on and on so I won't even start that discussion here, but just to say either of those would normally cover multiple rooms to around 75-100m^2 total area.

The safest option would be to get an electrician in to add the extra socket. If the cable is 2.5mm and not too much thermal insulation on its route they might decide to change the MCB to a 20A one which better serves several outlets.

A final note is socket outlets today should have RCD protection. Your existing distribution board may well have that, but it is something to check before deciding what to do.
Thank you for reply, we are RCD protected, but no room left in consumer unit. Changing the unit is another option, but we have limited space and it will be a separate question. Yes, extra socket can be added to the ring circuit, but it has to be done through the loft and it is much more complicated. My question were about two 2.5mm radials protected by one mcb, is it legal here?
 
Yes, it is acceptable to have two radials fed from the one MCB when it provides protection for the cable as this does. You might find it easier to take a spur off the existing heater socket rather than run another back to the CU.

However, you should note that adding a new circuit (add or change MCB value) to a CU, or changing the CU, is notifiable work under Part P of the building regulations covering England and Wales. For that you really should get a qualified electrician (a member of one of the competent person schemes like NICEIC) in to do it as it would work out cheaper than paying the building control folk to inspect/test and sign- off the work.

CPS members are able to self-certify their work due to their recognised qualifications & experience, so it is not a big extra charge.
 
Last edited:
Yes, it is acceptable to have two radials fed from the one MCB when it provides protection for the cable as this does. You might find it easier to take a spur off the existing heater socket rather than run another back to the CU.

However, you should not that adding a new circuit to a CU, or changing the CU, is notifiable work under Part P of the building regulations covering England and Wales. For that you really should get a qualified electrician (a member of one of the competent person schemes like NICEIC) in to do it as it would work out cheaper than paying the building control folk to inspect/test and sign- off the work.

CPS members are able to self-certify their work due to their recognised qualifications & experience, so it is not a big extra charge.
Thank you. It really helps our planing. Unfortunately we had a problem with electrician here when we had kitchen insulated. Job was done and all walls plastered and painted and when we wanted to buy a new kitchen, we were told that some part of the job was not done correctly according local regs. I had extra cost fixing it, plastering and painting. So now we plan ahead. Currently we have two 10 module units, night and day, we would like to have 22 module day one, but there is no room for it, we will still try to get as big as possible, but at least we need one module less.
 
That is a disappointing experience. For future work you might find someone on this forum near you who will do a much better job.

22 circuits is a lot by UK standards!

My flat has 5 circuits, and even then one is a former water immersion heater that now provides a single socket in the kitchen where it used to have an isolator switch!

As I hinted at before, the typical UK system is one RFC per floor for sockets, one radial (really a "tree") per floor for lights, and then a couple of dedicated radials for high demand loads such as a cooker, electric shower, etc. Perhaps one or two for external stuff like outdoor lights or a shed/garage feed.

So even a 3 floor house might only have 12 used!
 

Reply to Second radial line to 16a MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hate these. Been called out to troubleshoot a tripping MCB. It's a house I've been to before and I know the wiring is a real dogs diner, but...
Replies
19
Views
3K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, Our kitchen is going to be ripped out and replaced in the new year, and currently has just one small oven in it - I have 10 guests for...
Replies
26
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock