I’m carrying out a PIR on a three storey house (sheltered accommodation) with one lighting circuit for the whole property.


For the purpose of safety and convenience it should have two lighting circuits and/or have emergency light.



Would this warrant a code 4 or just a mention in the report?
 
Segregation of circuits refers to segregating LV and ELV circuits.
I think you are refering to division of circuits. In wich case you should consider Regulation 314.1 especially (i) avoid hazards and minimize inconveience in the event of a fault and (ii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit.
Applying a code 4 suggests that you do not consider the situation to be a danger, whereas a code 2 would suggest that the situation is dangerous, but not immediately so, but needs rectification.
 
Last edited by a moderator:

Reply to Segregation of circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
710
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
924
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi The ground floor of my house has two lighting circuits which are each protected by an MCB. One of those circuits is just indoor lights. The...
Replies
15
Views
4K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock