I'm testing a load of new builds and yesterday a little debate opened up between myself and another tester. First off he says segregation of safety circuits applies to the smoke alarms being completely seperate, for example not on the lighting circuit. It has to be on its own breaker entirely. I didn't say he was wrong because I wanted to look in the regs book to confirm first as is my nature but I can't see it anywhere. Is he misinterpreting it?

Secondly I refused to power up an installation and put tested stickers on the board until the main bonding was able to be connected when the incoming pipe work was installed. He quite aggressively told me I was F'ing wrong and that the sticker goes on the board when testing begins??? Now I'm 99.9% sure he's wrong there but before I tell him he is wrong I wanted clarification to be that extra 0.1% certain and tell him he is F'ing wrong.

I'm fairly certain on both these counts but I'm not pigheaded enough to ask for fellow pro's opinions.

Thanks for any clear clarifications
 
Smokes don't have to be on their own circuit, it is common to put them on the lighting circuit. An advantage of this is that the homeowner will notice straight away if the lighting circuit has tripped!

The main bonding needs to be present during testing, so that answers that I suppose.
 
Page 123 of electricians guide to building regs states it is actually preferred to have the supply for smoke detectors from a lighting circuit (if we are talking about a standard sized house, large house would be different)
 
Thanx for the response, that's what I thought on the smokes side, so the main question I have left is what is the exact reason for segregation of safety circuits, what exactly does it refer too?

And I it as 100% confirmation that the tested sticker goes on the board after it is comPleted satisfactorily.
 
Safety circuits are things like fire alarms, and security alarms. Smoke detectors as others state are normally fed from lighting circuits.
How can you complete a test on an incomplete installation? As you state you are doing an EIC if you complete this test you would need to fail the installation ans there is no main bonding. What you can do is the dead tests, record them and return when installation is complete to finish the live tests when happy sticker up. What if there was a cable snagged on a water pipe you may not it with incomplete bonding on a IR test.
If the installation is energised without effective earthing then there are potential hazards.
 
Segregation of circuits may refer to splitting circuits between more than one RCD, so if one trips, you still have part of the installation on.

Segregation of safety circuits refers to the actual cable runs - i.e. not running fire alarm cables, telephone, data etc. near LV cables.

And yes, put the sticker on when you've finished!
 
Thank you very much people. I shall now smugly go and correct him. Normally wouldn't be so smug but due to his aggressive curse filled rant yesterday because I disagreed with him I have no choice ::)

Much appreciate the confirmation guys/gals
 
"Commonly used Lighting circuit" ;)

Your man is half correct with regards to the smokes being on their own circuit - It can go on it's own RCBO or installed on a "commonly used lighting circuit"

As you know, if the lights go out people will know straight away.

The only time it will be known if the RCBO has tripped is when they go to check the test button at it's next quarterly interval lmao Or when the alarms start chirping because the batteries are running low.
 

Reply to Segregation of safety circuits? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
612
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
658
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
876
Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock