when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
 
if you are using the house earthing for the garage then the extraneous metalwork in the garage needs to be bonded to the house MET ( min 10mm )
 
hi

when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
Yes it is.
The two earth bars in the CUs become Earth Marshalling Terminals.
No the conductor doesn't have to be unbroken back to the house CU, or to the MET.
 
directly from met to each service ( water, gas,steel framework), or can you run a 10mm bonding conductor to garage cu and then bond garage extrenous conductive parts to the garage cu
yes...there nothing to say that the seperate 10mm earthing conductor to the C/U in the garage cant be the PME that you export....
 
so if you export the pme to the garage CU via the seperate 10mm bonding conductor would you only earth the supply cable at the house cu and not terminate at the garage cu ???? or just connect the supply earth as well
 
Last edited:
i take it your running armoured to the garage..?..yes?....if so then earth the armourings at the house end only......then use the CPC of the armoured together with the seperate 10mm earth cable together...parrallel em up..both ends...into the garage C/Us MET....then take the 10mm earthing cable you exported from there to extranious conductive parts within the garage..(water and gas)......keep it continuous...that is to say you go to the first extranious point...lets say gas....bare the cables insulation off....enough to terminate into a BS951 clamp..BUT DONT CUT IT...KEEP IT CONTINUOUS...then from there to the water...or vice versa...from water to gas...depends which service is nearer to the garage C/U of course...
 

Reply to seperate bonding conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
729
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
859
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock