Thanks very much. Very interesting what you did there to utilise the Cat5 cable. Unfortunately I don't think I be in a position to run a new cable out to the garage DB as it's a very long and difficult run(the older cable is buried underground with no way of pulling in a new supply as previous electrician didn't supply ducting.)You may be easier to run a new 16mm / 25mm {depending on cable calcs} to the garage (you could use a EV ultra cable), then you will have a CT line in the CAT5/6 back to the main supply as well as a ethernet one)
You could change the consumer unit in the garage and provide a seperate RCD for the EV.
Here's a diagram I made for myself to combine the CT and ethernet in a single cat 5
If you only use 1,2,3 and 6 for the ethernet the speed drops to 100M but it gives the other 4 cores to CT use.
View attachment 112479
I haven't visited yet to see what load is being drawn on garage DB, but say for instance if it was ok to come off garage BD for supply to charger, and have CT clamp at incoming garage supply cable, do I have to have another CT clamp at the main DB in the house? If so, then why?
Thanks.