10
Hello, everyone

I want to install a second unvented hot water cylinder.

The existing (indirect) dhw cylinder has a backup immersion heater on a dedicated circuit with a timer. The immersion is timed to come on overnight, but usually does nothing as the boiler keeps the water hot enough so the immersion thermostat never turns on unless the boiler goes out (not often, but not unknown either - usually due to an empty oil tank). This way, we always have hot water to wash with in the morning,

I want to install a second direct unvented cylinder in a completely different area of the house.

The existing immersion circuit is re-purposed from what was once a radial circuit run in 4mm to power an outbuilding (long demolished), and runs right past where I want the second cylinder.

Can the second cylinder share the immersion circuit? There is/will be nothing else on the circuit.

I know that immersion heaters are supposed to have dedicated circuits, but it doesn't explicitly state that they need one each.

Thanks.
 
Hi - it may be possible, but first a few quick questions :)
  • what is the installation method of the existing 4mm cable?
  • what is the existing circuit breaker rating?
  • what are the two immersion heater kW ratings?
 
Hi - it may be possible, but first a few quick questions :)
  • what is the installation method of the existing 4mm cable?
  • what is the existing circuit breaker rating?
  • what are the two immersion heater kW ratings?

Hi thanks for replying

Installation method is mostly clipped to joists on the attic under 100mm of insulation. About 3 feet is in conduit through several walls
MCB is B16 (Square D)
The existing immersion is 3kw, as will be the new one.

Obviously I will have to change the breaker - based on the wiring in the rest of the house, a B32 should be OK (there are other radials in 4mm on 40a RCBO's)?

Assuming it's OK, I'll be putting each one on a DP switch so I can isolate them individually for servicing.
 
As soon as you mention that the cable is under insulation there may be a problem. The 4mm cable exceeds 32A if it is clipped direct in free air, but not under insulation, sorry.
 
As soon as you mention that the cable is under insulation there may be a problem. The 4mm cable exceeds 32A if it is clipped direct in free air, but not under insulation, sorry.

OK. If I either re-route or more likely re-run in 6mm, can I share it or should I pull in another 4mm? There is a spare way in the CU but I was trying to avoid creating a new circuit. Running another cable will be a pig to do - access isn't great.
 

Reply to Shared immersion heater circuit? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters. I was hoping to use the same circuit the my existing tank...
Replies
16
Views
2K
Hi everyone I have 2 x 250 litre unvented indirect DHW cylinders. The primary heat source is the oil fired boiler, but both cylinders have backup...
Replies
0
Views
985
Can I supply my central heating (programmer, two port valves and boiler) via a fused spur taken from the immersion heater circuit? They’re...
Replies
18
Views
3K
We are replacing our Economy7 hot water cylinder due to a leak that has two immersion heaters and an indirect coil from our multi-fuel stove. My...
Replies
3
Views
1K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top