Discuss shaver socket in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
7
hi, in part p, it says there is no socket outlet within 3m of a bath, however shaver socket is an exception,why is this, what the main difference of the shaver socket? sorry for this silly question.

cheers
 
Shaver sockets are 230/110 volts and are not SELV, remember Extra Low Voltage is 50V or below . A shaver socket has a double wound isolating transformer. This means the socket is electrically separated from earth, allowing you under single fault conditions to touch a live conductor and earth and not receive a shock. (Because there is no earth path)

crossfig2_l.jpg
 
Last edited by a moderator:
Electrical seperation is the keyword.....roukel's post explains it well. A shaver light/socket contains an isolating transformer in which it's secondary winding is completely isolated from the earth of the supply circuit, thereby eliminating the path to earth for shock current.
 
Last edited by a moderator:
Well I have stood on a rubber isolating mat and touched a 240v live conductor (Same principle ie no return path) and I didnt feel a thing not even a tingle. Mind you a sparky I was working with did it first, just to prove his point. All was fine until I shook his hand.:eek::eek::D

Ps, NOT RECOMMENDED.
 
Just out of interest, has anyone ever tried out the theory, and touched the live of an isolating tranny?!

Never touched one, but measured it on a boat's shaver point that was being fed by a 2.5kW modi sine inverter. These have fundamentally diferent characteristics to land-based mains power.

The secondarys of that isolating tranny had a line-earth potential of more than 70VAC!!! Enough to give a tingle for sure.
The line-line potential was 270VAC.

Anybody measured the same on a household shaver point?
 

Reply to shaver socket in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, after some discussion with electricians, does removing a 16A or 32A socket constitute safe isolation? I understand that removing the socket...
Replies
8
Views
491
I'm about to do wiring for a small apartment in Azerbaijan. Mostly I will try to use UK standards - ring mains with ELCBs, everywhere earthed, T&E...
Replies
10
Views
3K
Good afternoon I have recently had a bathroom makeover and had the existing shaver socket removed as I purchased a cabinet with socket enclosed...
Replies
10
Views
3K
hi there - Im about to book an electrical safety certificate for a property that will be let out and I notice I have plug sockets in the bathroom...
Replies
18
Views
4K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock