Main reason was because the main switch is 63amps, I know that means that's what the switch can handle not what SHOULD be fed before anyone jumps, I've got a 20amp mcb and a 6 amp so a 30 amp mcb from the house would do on 4mm if I'm not right correct me?

Depends on the type of cable and where/how it is installed. You may need 6mm or bigger if the type of cable and other factors require it
 
Ib<In<Iz for a start. now tellus what cable and OCPD.
 
I've ran my 6mm cable, positioned, fixed and terminated all cables into the shed CU

Thought you already had your 6mm in place? ?.
 
Main reason was because the main switch is 63amps, I know that means that's what the switch can handle not what SHOULD be fed before anyone jumps, I've got a 20amp mcb and a 6 amp so a 30 amp mcb from the house would do on 4mm if I'm not right correct me?
20A is more than enough for the capacity you require so for a 10M run you could have used 2.5mm 3 Core SWA.
Required Cable Size2.5 mm
Voltage Drop2.61 Volts.
Percentage Drop1.1%
Current Load17.4 Amps
Max Cable Load[SUP]*[/SUP]21.4 Amps
 
You have a 20amp and a 6amp MCB? Simply double them up and hey presto you've got a 26amp MCB!
are you part p registered?
As owner and installer you will be doubly screwed if not
 
I want to put a 2 way consumer unit into my shed to feed 2 outdoor sockets and a couple of spot lights.

I have bought the CU with a 63 A main switch, 1 x 20 amp for sockets and 1 x 6 amp for lighting,
now my question is, can I take a supply from my kitchen socket (fed from a 16 amp mcb) through the wall to the shed in 2.5 mm or 4.mm cable into the 63 amp main switch?

If that's not sufficient then what size cable to go from my house CU to shed CU (under 20 meters away) and can i connect that to a 35 amp mcb or do i have to connect it to a 63 amp?

I don't want to do a FCU as I may add more lighting in the future and a CU looks neater.

Thanks, Ryan.
The more I read this the more I despair, as the thread has moved on I have read your posts and then looked back at this, is this post correct or are we still with the 6mm2 cable in on a 32 amp MCB now? or is it a 35 amp and a 4mm2? is the run 7 mtrs or 20? what about the extra future lighting load? or are we at the 2.5mm2 off the ring circuit? confused . com here.
 
Well I don't have to I'm going to leave it but I meant that 4mm cable could handle that load

No that's not what you said.
This whole thread is poppycock, balderdash, claptrap and piffle. And for that reason...I'm afraid I can't invest any more time here, so........ I'm out.
 
Well I don't have to I'm going to leave it but I meant that 4mm cable could handle that load
To be a good liar you have to have a good memory Ryan. I too am now convinced this is all BS. Congratulations on sucking a lot of people in, I hope you enjoyed yourself.
Oh and welcome to my ignore list, you're in good company on there.
 
to be fair I never thought of looking back through my stuff, it was just a pretty basic question that could have had a basic answer as it is only basic work!
It's very basic work but the consequences of getting it wrong are potentially dangerous or even lethal.

yeah I've got a multi meter but have access to a MEGGER so thats not a prob........
You don't have sufficient test equipment to work safely or test the installation correctly.


I'm closing this thread I'm afraid, I've got serious doubts that you're working safely and can design this safely. I'd suggest getting a more experienced sparky to shadow you on this job to refresh your skills you learned several years ago. It might mean you don't make profit on this particular job but it would be safer for the customer and you'd benefit in knowledge.
 

Reply to Shed/Garden Electrics? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
989
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
880
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
342
I've been retired a few years now so no longer active in the industry, but I've been doing electrical "stuff" for most of my life. Trained as a...
Replies
3
Views
315

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock