Discuss Should internal links in consumer units be double insulated where TT earthing is present in the UK Electrical Forum area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
 
Best to use an S type 100ma RCD main switch with a tails gland making sure it enters as close as possible to the incomer. Internal links are then covered. If you are using RCBO's they must be DP or switched N if you have an RCD main switch.
 
has anybody ever seen internal links damaged and shorting out to a metal case CU? I certainly haven't.
 
No I’ve not seen any insulated and sheathed internal cabling. Nor have I seen internal links flailing about, but it is a possibility I guess.
 
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
 
Last edited:
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
No it’s a main switch with rcbo’s or dual rccb’s with an S type upfront is what they mean, ( I think).
Not very clear but that would make more sense.
30FDBE3B-FEAF-4DEF-A239-6340054ED0FA.png
 
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
They aren't double insulated they are insulated and Mech protected, never seen a cable with the double insulation marked on it.
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
I think radiohead's point is if a final circuit has a N-E fault then you will probably trip the incomer RCD as the SP RCBO will trip but not isolate the neutral fault.

So it is not necessary according to the regs as such, but it is far better to have a N-switching RCBO if you can. I guess it indirectly comes under the requirement for selectivity, etc (off hand don't remember the numbers).

Not that many do unfortunately, but at my last count Wylex/Crabreee/Fusebox (the miniature version) RCBO for consumer DB do switch neutral.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966
 
Back to the OP's point - I really think that any properly installed metal CU is going to be fine.

I.e. where the tails are double-sheathed as expected, they enter by a proper gland for support and protection from damage, and the CU has been installed with care to make sure the busbar is in place and clamped correctly, etc.

Obviously all circuits have to be RCD protected as TT rarely will have a Zs able to disconnect a MCB, and at that point I would state my personal preference for both an up-front 100mA/300mA delay RCD and then whatever 30mA instant RCD/RCBO are needed for "additional protection".

In my case it is less about the risk of an internal CU short, than about the risk of a 30mA RCD failing to trip and so the earth/CPC remains live for a prolonged period. With an incomer RCD there is no single point of failure.
 
Last edited:
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966

When were Wylex/Crabtree SP&SN RCBO's first introduce? I have a feeling that many TT installs have been none compliant since July 2015, if that's the case.
 
In what way ?
I’ve never seen an rcbo board with an RCCB as a main switch

I have sort of. But I've also seen a CU with RCBO's and a main switch, suitable for use with TT supply, as detailed in OSG (yellow) figure 3.6.3. My point is, there were very few if any DP RCBO's or SN back then.
 

Reply to Should internal links in consumer units be double insulated where TT earthing is present in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
967
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
I was called out to a fault today where the newly fitted consumer units RCD was tripping when the cooker was switched on.The cooker had been...
Replies
39
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock