Hi all, looking for some input from you guys. Had a call out a few days ago where someone has has a shock from brass light switch in a domestic property. When i got there, a decorator told me that he had the switch loose from the wall to strip the wall paper. He's used a steamer, so it points to moisture getting into the switch. The woman who lives there then went to use the switch later and got a shock. Apparently quite painful. The lighting circuit is covered by a 6a mcb on the non-rcd side of the board. When i got there, the switch must have dried out and was functioning fine. I did a ZS at the switch (my megger 1741+ allows a 2 lead test) and i got a reading of 0.69. The CPC was connected to the earth terminal on the switch. So, should the MCB not have tripped?
 
She may well have but her body resistance and the damp will have a high resistance which would have restricted the current flow.
 
MCB would not trip.a RCD may have done, if fitted. bear in mind that a 6A MCB requires approx. 30A fir instantnneous trip. shocking,innit?.
 
She may well have but her body resistance and the damp will have a high resistance which would have restricted the current flow.
I always think back to when i was a young'n and i was getting a tingle of a machine we had in for service. No one believed me as i was the only one, till the gaffer tested it and low and behold.... Fault!
 

Reply to Should the MCB have tripped? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
946
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
45
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock