Discuss Lighting MCB keeps tripping after changing the kitchen light in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
A.jpg


I'm not sure what's going on with my kitchen light.

I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from Screwfix). Although the light turned on after flicking on the MCB, when you turn it on or off the MCB trips, and sometimes the RCD, too.

I removed the bulbs to see if they were the cause, but the issue remained. So I removed the fitting, too. The MCB still trips.

In all the light fittings I've previously installed I've always twisted together the live and neutral wires - but although I've done it here to fit the block in the new fitting, in the original fitting (picture B), the only wires twisted were the earths.

I'm not sure whats going on, but by a process of elimination, twisting the neutral and live wires is obviously caused the MCB to trip - nothing else has changed!

I didn't take a picture of the original fitting as I wasn't expecting problems, so I'm not sure how to rewire it. Looking at the available connector - which has two holes labelled N, and 2 labelled '1', I assume these are for the separate neutral and Live wires. Having a plastic body, the earth wasn't needed?

Any help or explanation of what I'm doing wrong would be welcome. :)
 

Attachments

  • B.jpg
    223.5 KB · Views: 22
  • C.jpg
    294.3 KB · Views: 23
In all the light fittings I've previously installed I've always twisted together the live and neutral wires
You have been lucky up until now.
It is frequently the case that one cable 'delivers electricity' and another cable is connected to a switch.
(Sometimes there is a 3rd cable to deliver electricity on to the next room)

It seems almost certain that one of your cables is the supply, and one is connected to the switch. If you just join them together as pictured you are shorting out neutral and live when the switch is on. You should really have paid more attention to what you removed.
You can't make this work with what you have there, another connector block (Wago / choc block) is needed as well as tester to determine which cable is which.
 
So the switch for the kitchen is 3 gang, but the MCB only trips if the kitchen light is turned on. I've just untwisted the wires - so the neutral and live wires are now separate - and the MCB no longer trips when you turn on the switch.
So I assume this switch only turns the one light on, if so you have a scenario are described by @timhoward above.
 
You have been lucky up until now.
It is frequently the case that one cable 'delivers electricity' and another cable is connected to a switch.
(Sometimes there is a 3rd cable to deliver electricity on to the next room)

It seems almost certain that one of your cables is the supply, and one is connected to the switch. If you just join them together as pictured you are shorting out neutral and live when the switch is on. You should really have paid more attention to what you removed.
You can't make this work with what you have there, another connector block (Wago / choc block) is needed as well as tester to determine which cable is which.
Thanks, Tim. I've been reading up and thought something like this had happened. It might not be luck - I think most of my wiring experience is using 1960s-era cabling...

So a voltage detector pen will tell me which grey cable is the supply, and which is the switch (I also have a multimeter).

I'm not clear how a block would make the fitting work, though. Do I just need a different fitting?
 
Thanks, Tim. I've been reading up and thought something like this had happened. It might not be luck - I think most of my wiring experience is using 1960s-era cabling...

So a voltage detector pen will tell me which grey cable is the supply, and which is the switch (I also have a multimeter).

I'm not clear how a block would make the fitting work, though. Do I just need a different fitting?
I would suggest you need an electrician.
 
I do appreciate that. I think I've worked out what I've done, and how to fix it. Before wiring that, though, I'll draw a diagram and post it here tomorrow to check I have understood things correctly. If someone could confirm it's correct, that would be welcome.
 
Although I agree that this is a “supply” cable and a “switch” cable…. I am surprised it wasn’t noticed when you took the old fitting down that the two browns were together, not connected to the light…. and the two blues were across L and N.

I am also thinking now that wiring like this, with a dead short across the switch when operated, has possibly damaged the switch, and/or the circuit breaker. Especially if it’s been done a number of times.
 
Top tip, though too late now, is always photograph what you are about ti disassemble. And again after reassembly.

It helps if something unexpected happens and you need help, and it also serves as a record of when something was fixed should you need to replace a failed accessory, light, etc, and suspect it should still be under warranty.
 

Reply to Lighting MCB keeps tripping after changing the kitchen light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
696
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
891
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
879
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock