Discuss Shower Problem. in the UK Electrical Forum area at ElectriciansForums.net

H

highspark

Was sub contracted in by a plumber to replace an electric shower. Old shower was going hot and cold intermittently. Plumber assumed the shower was knackered and told me to replace it like for like. No cable installation just a straight swop. Also as soon as shower was turned on lights in the flat were dimming slightly (volt drop?). I have not been able to rectify the dimming but I am presuming there is a loose connection somewhere?

Anyhow, brand new shower now has the exact same problem hot and cold intermittently. I'm totally lost to why this is happening. Plumber assures me that the water pressure is fine. However cold feed loops up and back down on itself then connects into the shower. But plumber isn't having it though. The fact that the same thing is happening on a brand new shower as on previous shower leads me to believe there is a problem elsewhere?

any ideas?

8.5kw shower ran in 6mm, clipped direct, 32 amp breaker

old persons residential apartment.
 
with the shower running hot, flush the bog. if it goes cold then it's the water pressure.
 
This is a long shot but we had a triton shower doing the same thing. Changed it still the same issue. Read up on it and it had a minimum pressure output. There was a small filter in the shower head that the cleaner had changed during his shower head disinfection. Took the filter out and it was all good
 
normally water pressure , lights can dim slightley when you slap 8.5kw same as the main supplies light tend to dim at 8.00 when corrie finishes and there a surge of people switching kettles on
 

Reply to Shower Problem. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Bit of a strange one ive been told by everyone ive called had a triton t70xr 8.5kw The water started running cold like the tco kicked in after a...
Replies
3
Views
2K
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
965
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Hiya, Had a Triton T80 8.5Kw shower for the last two years in upstairs bathroom connected to the mains cold supply. Its still working but...
Replies
44
Views
7K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock