Discuss Siemens RCCB trips even while inductive motor is off in the Electricians' Talk area at ElectriciansForums.net

Reaction score
4
Good day everyone

This is my first thread here, and I'm writing because I have a problem which I'm not sure how to solve. Since its company money, I just want to make sure that the conclusion to the problem is correct.

We have an autoclave that works at 121 celsius to sterilize with steam. Its equipped with a vacuum pump of 2 HP which draws around 8.5 A with 208 V. The power comes on direct line (No VFD), through an RCCB 0.1A and 25A power surge.

The RCCB keeps tripping on a specific point of the process and even goes off while the motor is off. We use a normal 4x1.5mm cablet (3power 1ground), no shielding. The insulation is new (we just painted with dialectric paint the stator of the motor, changed bearings and clean it).

Is it parasitic capacitance of the cables?
Is there a leak through the stator?
Or the RCCB is damaged?

If you guys need more information let me know.

Thanks
 
Good day everyone

This is my first thread here, and I'm writing because I have a problem which I'm not sure how to solve. Since its company money, I just want to make sure that the conclusion to the problem is correct.

We have an autoclave that works at 121 celsius to sterilize with steam. Its equipped with a vacuum pump of 2 HP which draws around 8.5 A with 208 V. The power comes on direct line (No VFD), through an RCCB 0.1A and 25A power surge.

The RCCB keeps tripping on a specific point of the process and even goes off while the motor is off. We use a normal 4x1.5mm cablet (3power 1ground), no shielding. The insulation is new (we just painted with dialectric paint the stator of the motor, changed bearings and clean it).

Is it parasitic capacitance of the cables?
Is there a leak through the stator?
Or the RCCB is damaged?

If you guys need more information let me know.

Thanks
If I was you I would take a close look at the motor you took apart. Did you have problems before you took the motor apart?
 
Good day everyone

This is my first thread here, and I'm writing because I have a problem which I'm not sure how to solve. Since its company money, I just want to make sure that the conclusion to the problem is correct.

We have an autoclave that works at 121 celsius to sterilize with steam. Its equipped with a vacuum pump of 2 HP which draws around 8.5 A with 208 V. The power comes on direct line (No VFD), through an RCCB 0.1A and 25A power surge.

The RCCB keeps tripping on a specific point of the process and even goes off while the motor is off. We use a normal 4x1.5mm cablet (3power 1ground), no shielding. The insulation is new (we just painted with dialectric paint the stator of the motor, changed bearings and clean it).

Is it parasitic capacitance of the cables?
Is there a leak through the stator?
Or the RCCB is damaged?

If you guys need more information let me know.

Thanks
Call an Electrician to do some testing of the Motor and the wiring.
 
As Pete999 says do some testing of the motor insulation resistance but from what you described, the RCCB trips even when the motor's DOL contactor/starter is open - yes? That the RCCB does trip when the DOL is open indicates the problem is elsewhere.

Does it always trip at exactly the same point in the cycle? If so what happens at this point of the cycle? Do an IR test on the heating elements and ampclamp the live conductors when they are on and also the earth/cpc to them. It could be these elements are failing/have failed.

Or did you mean that when the contactor/starter opens the RCCB trips?

The other tests to do are to measure with an ampclamp to measure the leakage current in the earth/cpc and the residual current in all three line conductors. For the latter do it to the whole machine and other sub-systems of the machine.

Does the RCCB only supply the autoclave or other circuits as well?

Please post a drawing of the wiring would be very helpful to folk of the EF to 'set the scene' and for them to study - pictures are often helpful too.

Pay particular attention to the possibility of tracking between live conductors and earthed metalwork. Dust, water, cleaning agents, debris can all start off and promote tracking so it would be a good thing to thoroughly inspect and then clean away such dirt and detritus.

What is the earthing system? TT, TNCS, TNS...?

Last for now - are all connections good electrically by being clean and tightly secured? Try the tug and wiggle test on them all. This includes connections before and after the RCCD.
 
WhatsApp Image 2018-10-11 at 8.28.34 PM.jpeg

I also noticed yesterday that the Test button does not work, does this mean the RCCB got damaged?

WhatsApp Image 2019-08-22 at 9.53.29 AM.jpegWhatsApp Image 2019-08-22 at 9.53.29 AM.jpeg
As you see in picture 2 with the message POWER FAIL, it means the RCCB went off while the motor was not working. But the DOL stays close, so current can flow.

In picture 1 you can also see when it usually the RCCB goes open.

To clarify at this moment, I don't have a Megger nor the purchase of one will be approved. Is there a way to test insulation without one?

1566490092775.png
This is the electrical diagram the currents displayed are not correct. The OLR1 (The RCCB) is as specified in the picture before and that is what goes open.

To answer also megawatt, the motor used to trigger the RCCB a lot more often, after we painted the stator, it only happens randomly and usually at the point in the process where I already specified (Picture above).

As you may notice I am not an electric Engineer but and Industrial Engineer my knowledge is not so advance as you.

Hope the attachments help.

Best regards
 
ONLY DO THIS IF YOU FEEL SAFE TO DO IT AND HAVE SOMEONE IN ATTENDANCE

Do you have a test equipment to measure ac voltage up to say 450V and do you know how to use it safely? If you do could you measure and tell us the following voltages:

L1-L2
L1-L3
L2-L3
L1-N
L2-N
L3-N
N-E
L1-E
L2-E
L3-E

For my EF colleagues this RCCD uses L3 and N for the test function. See page 6/30 of:


My initial thought - test button does not work - > somewhere(upstream?) an N conductor fault/missing/loose/lost? (-> assumes DOL takes(tbc) its coil supply line to line so remains closed and motor will run while 3 lines energised/stops when RCCB trips.)
 
Last edited:
PS: Second thoughts on my initial thoughts :) OP said DOL remains closed when RCCD trips...
As shown in the electric diagram, first comes and MCB of 25A, then the RCCB also of 25A. The only thing that trips is the RCCB. The equipment detects the trip and stops the process. As I previously said It also tripped when the motor was not ON.

My current thought following marconi ideas is to constantly measure earth line from the motor to check if I actually have a leak, if not leak I'll try just to change the RCCB for a new one.
 
Thank you Nicelectrician. Do work safely at all times.

Your measurement readings are very useful to us in helping you. Please be careful to describe the measurement you are taking and the circumstances of it (ie what is or is not on/off, running/stopped). Those voltage and IR measurements I mentioned are typical standard first checks to do so if you can safely do them that would be great.

What is definitely wrong is that the RCCB does not trip when the test button is pressed.

What is the temperature in the electrical cabinet?

There is no harm in doing low voltage insulation resistance(IR) checks using a multimeter set to Ohms of motor winding or heating element to earth and between windings of the motor, but the proper way would be using a proper 250/500V IR tester such as a Megger if you can get or borrow one. Please report any measurements you take. Remember safe isolation before you do any testing and have someone standing by you. Wear electricians rubber gloves near exposed live equipment and remove watches, bracelets, rings, etcetera.
 
Last edited:
I have read again what you said in your #8. You wrote:

This is the electrical diagram the currents displayed are not correct. The OLR1 (The RCCB) is as specified in the picture before and that is what goes open.

I need to check what you mean to say. In #8 you say that the motor's protection Overload Relay OLR1 trips but then you mention and have shown a picture of a different electrical device - a Residual Current Circuit Breaker(RCCB): They are not one and the same device. The RCCB will be before the Miniature Curcuit Breaker MCB1.

If OLR1 trips then the motor has drawn a sustained over current in one or more lines (L1, L2, L3). If the RCCB trips then there is overall an unbalanced/residual current flowing (to earth) across L1, L2, L3 and N through the RCCB. Could you confirm OLR1 trips as well? If it does then there are a number of reasons why this could be happening.
 
Could try to find out and provide a circuit diagram for how the autoclave's computer/controller monitors the incoming power supply to detect a power failure?
 
Could try to find out and provide a circuit diagram for how the autoclave's computer/controller monitors the incoming power supply to detect a power failure?

Most common way of monitoring a tripped device in these situations is to include an auxiliary volt free contact onto the motor protection circuit breaker, or in this case RCCB.

I'm still trying to understand, which device is actually tripping.

An if the contactor is closed when it does. One post suggests when the motor is running, the other suggests that the contactor is closed even when there isn't power?

He also suggests that OLR1 is an RCCB, if this is the case, it is not offering correct protection to the motor.

I imagine this problem would be rather quickly fixed with a few tests using an insulation tester. OP says there is no funding for this, ask your boss/manager, how much is downtime costing him?

A decent top end insulation tested will be around £400 but can be gotten for <£100. Take a look here, also I believe a forum member discount can be gotten:

 
There is a thermal overload shown in the schematic. How come this is not fitted?
 
Nicelectrician: You wrote in your first post:

We use a normal 4x1.5mm cablet (3power 1ground).

by which I understand you provide L1, L2 and L3 and an earth/cpc to the autoclave.

But the image you show of the RCCB shows L1, L2, L3 and a neutral - to the far right of the four terminals top and bottom - there is a black conductor going in and not out. This indicates to me that the autoclave requires a four wire 3 phase supply - L1, L2, L3 and N plus an earth/cpc.

The fact that the RCCB trip test button does not work also indicates the N is absent.

I think then that you should check the installation instructions to confirm whether a Neutral is required - because I reckon it most certainly is.


At the stage of the autoclave process, the sterilisation has been completed and the chamber and its contents are now being rapidly cooled by a number of cycles of vacuum pump on, vacuum pump off(hold), vacuum pump on, VP off(hold)... see:


If the autoclave uses a water cooled cooled jacket system to reduce the the chamber temperature, there is either a small water pump being turned on/off to circulate cold water or an electrically operated solenoid valve is opening/closed to do it. The pump or valve may be the only electrical part of the autoclave which require a Neutral. The absence of the supply neutral only becomes a problem then the first time they are energised by the autoclave's computer/controller.

(For my EF colleagues, I suspect there are other light current loads using a neutral, the net effect being a virtual neutral is produced which is good enough for them until the higher current required by the pump/solenoid I mentioned in the previous paragraph disturbs its potential wrt the lines and earth and then transient leakage currents trip the RCCB or the residual current over the 3Ls and N through the RCCB sense coil - the virtual N being on the load side of the RCCB -or something along these lines.)
 
Last edited:
Hello All

Thank you for your quick response. First I need to apologize, I did not check in person the electric cabinet until now. I will have to fire my "electrician" or re-evaluate him. He told me incorrect information which I provided to you EF. I have attched the whole manual, from page 178-196 are the electric diagrams.

Also the RCCB does indeed feed not just the motor but other components, L1 and L3 goes to other components. I will check them personally later. I tested the motor the insulation is ok and the loads are balanced when I tested the motor outside the machine.

WhatsApp Image 2019-08-23 at 2.43.17 PM.jpeg

So from now on, I will provide tested information by me.

Again huge thanks to Marconi and everyone who are at this moment teaching me with just comments on the problem.

Best regards to you all
 

Attachments

  • Operation Manual Steam Sterilizer (1).pdf
    6.2 MB · Views: 8
Ahh one more thing this is an Indian low-cost machine, I already told management that this machine is not new but used or it got wet during shipment, the motor is not by close new, not even second hand, super used. They told me to just keep repairing it to make it operative.

Thanks again
 
Page 179/196 details how the 'Power Fail' signal is produced. Monitor its state at the relay and also at the input to the PLC.

The Autoclave does require a Neutral so a 5 wire cable to it.

Have you really connected N to ground at the output of the RCCB? That would not be right to do.

There is a power supply filter which may have failed/is failing - has the problem only just started after a period of trouble-free operation? (see the page with the wiring diagram which shows the RCCB).

Do the checks suggested and of all other power supplies eg: 24V ac and 24 dc. Pay particular attention to check and test components I suggested and others which only come into use after the Sterilise phase has ended and the cool down starts eg: vacuum exhaust valve.

I am off to bed now. :)
 
The same transformer that provides the supply to the 'Power fail' relay has another secondary coil which provides the 24V ac for the various electrically operated solenoid valves(V1 etcetera). The load of one or more of these valves being energised could be loading the transformer such that the voltage to the 'Power fail' relay has a temporary dip, opening it's contacts briefly, and then recovering to close the contacts - yet the PLC detects the brief opening of the contacts and assumes a 'Power Fail' has happened.

Check the output voltages of the secondary coils and also any marking for the voltage rating of the primary coil - is the primary suited to 208V or is it a 220V/230V/240V primary?
 
The same transformer that provides the supply to the 'Power fail' relay has another secondary coil which provides the 24V ac for the various electrically operated solenoid valves(V1 etcetera). The load of one or more of these valves being energised could be loading the transformer such that the voltage to the 'Power fail' relay has a temporary dip, opening it's contacts briefly, and then recovering to close the contacts - yet the PLC detects the brief opening of the contacts and assumes a 'Power Fail' has happened.

Check the output voltages of the secondary coils and also any marking for the voltage rating of the primary coil - is the primary suited to 208V or is it a 220V/230V/240V primary?
The situation is that the RCCB actually trips.
 
You have not answered whether the supply has a neutral.

Also you have not confirmed whether the neutral at the RCCB has been 'grounded' which I said was wrong.

You have not yet measured any voltages as I asked.

:-(
 
The RCCB may not be faulty. It is certainly not correct and potentially dangerous to connect - as said in the image below the lower terminals in #18 - the neutral from the RCCB to earth/ground (especially since there is a filter in the supply lines - forgive me but I will not explain why).

The wiring diagrams I have looked at show no neutral coming out of the RCCB only one going in to it - see page 178 of 196 in manual.

Could you/your company not buy one of these:


The autoclave requires a 5 wire supply providing L1, L2, L3, N and E - HAS IT!!!!!!!!! If it does not then the first thing to do is provide a 5 wire supply with a neutral.

I am becoming exasperated with you hence the bold annoyed text.
 
Last edited:

Reply to Siemens RCCB trips even while inductive motor is off in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock