Discuss Simple job? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Scenario: "I'd like a single smoke alarm hard wired in my house so I don't have to worry about changing the batteries if I decide to rent it out in the future" says the customer.

right, smoke alarm in hallway off of upstairs lighting circuit, 0.5m away from ceiling rose. So far so good. Check CU... 2 b6 mcb s for upstairs and downstairs lighting, not protected by rcd. Ahhh. Will require an RCBO as well. And it's notifiable works. check lighting circuits... Looks like there's a borrowed neutral...

So the options I see are: surface trunk the new smoke across the ceiling (won't be an option for most customers) so no rcbo needed; or run an earthed metallic sheathed cable (is there a cable that's practical for this?);or put both living circuits onto one rcbo if loading is appropriate and wire smoke normally; or start ripping the house apart feeding new cables for the lights and putting in new RCBOs for lighting circuits.

A quick cheap job turned into an expensive one, or am I missing a simpler way to do this?
 
So no RCD protection is required, no notification to building control is required.
The borrowed neutral should be sorted but is not part of your remit, but probably good practice.
Run 0.5m of cable from light fitting to smoke alarm, test your part of the circuit, recommend residual works, done.
 
If you think about it, running the new cable will involve going UP - into the loft (if I've read the OP right) - where it effectively becomes a surface run.

And generally speaking there's no need to provide RCD protection to smokes and alarm panels (in fact there are some distinct disadvantages), so long as the cables have been run correctly - and as the outlets are normally to be found on ceilings........
 
Why not tell the tight arse skinflint wannabe amateur landlord to do a proper job and fit a proper interlinked system with a couple of smokes and a heat alarm. Then at least if he does embark on his tinpot landlord business, his prospective tenants will be properly protected, and in the meantime he will as well.
 
Going to sound really stupid but currently sub contracting to council on/off and any circuit worked on/ new circuit even if surfaced mounted in trunking has to have rcd protection or would this just be there guidelines. Don't question it as fitting an rcbo is an extra £12.50 n mains change £25 megga bucks
 

Reply to Simple job? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
634
Just had a simple kitchen light not working job, one of the fittings with the 4 spotlights on it. Took the fitting down to check if there was...
Replies
7
Views
976
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
507
Hi all, Just wondering what the general situation is with other people on smaller jobs, do you give a quote or estimate to the client before you...
Replies
6
Views
999
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock