Discuss Single phase distribution for small flats in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
im in the process of pricing a small flat development (sheltered accommodation/safe house. type thing
It's a 2 storey mid terrace. Being converted to 6 bedroom with small en suites. Shared kitchen diner.

Initially I told the developer they need a 3 phase supply as electric showers and heating specified etc.

Since then they have fallen over with price getting said supply!

So now all hot water and heating will be from gas boiler etc.

So I have spencer the following

Supply is in cellar as per usual terrace 100a
12 way board
X6 32a feeds for each bedroom (only have 4 sockets and 3 low energy lights) mining board with rcbos
-kitchen ring
-oven
-hob
-kitchen lighting and landlords areas( hallway stairs)
-boiler supply

Just running it by you guys as a way of getting round the job spec.
Or should I insist on least another single phase supply.
I don't see it a load issue with the nature of the building use.

Any pointers much appreciated
 
Hi - With proposed use in mind, plenty of smoke and heat detectors and maybe some emergency lighting in hallway. Think about how much bonding will be required - will one gas and one water suffice now there is many bathrooms (hopefully ok). TV sockets into br and common area? FWIW I agree 100A supply with gas heating and hot water is likely ok, but I would confirm final design with calc from OSG appendix A. This will take a little thought, as using the general table A2 the proposed 6 bedroom rfc with diversity comes to 32+0.4*5*32 = 96A. You don't want to buy a bunch of 32A RCBO and install 6 rfc only to decide later that 20A would be better and it could've all been radials. Just some thoughts. Cheers, David.
 
i'd run a 20A radial for each room's sockets. put the lighting on 2 circuits ( one for each floor ), a bit of overkill to run each room's lighting on it's own circuit.
 

Reply to Single phase distribution for small flats in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Replies
4
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Got called to "a flat in Manchester has no hot water" at 16:30 today and to be frank I was a little miffed to have to attend. So arrives at site...
Replies
67
Views
7K
This will be very vague as dont have many details... BUT ill relay what I can from what I'm told... so someone has asked me to wire a flat above...
Replies
4
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock